Omer,
I would set ERV-LATENT-EFF to 0.50.
Additionally, if the baseline system is required to have an economizer
per G3.1.2.6, I would meet the G3.1.2.10 requirement "to bypass or
control the heat-recovery system to permit air economizer operation,
where applicable", by setting ERV-RUN-CTRL to WHEN-MIN-OA.
I guess it is a judgment call how to set all the other ERV variables.
Typically, I set them identical to the proposed ERV if there is one.
Regards,
Bill