Jeff,
There are a number of workarounds for modeling DOAS units in eQUEST. The latest eQUEST beta version can run DOE-2.3 which has explicit options for modeling DOAS systems. A single DOAS can serve multiple other systems and be configured to supply the zones directly or to connect to the mixed air, as in your WSHP case. I don't have much experience with it but it looks promising.
For fan power, it sounds like you have sized the DOAS already, so the 20HP supply and 7.5HP return fan power (or better yet, the BHP for the fan selections) should be entered via some combination of inputs instead of letting the system(s) be autosized. If you specify HVAC-SUPPLY/RETURN for ERV-FANS, then any fan power entered in the Heat Recovery 2 tab inputs will be added to the fan power entered for the system SUPPLY-KW/FLOW or SUPPLY-STATIC. The fan power penalty for the ERV section appears in the ERV Energy Recovery Summary reports. I would also look at the SV-A and SS-H reports for the systems in question. You could multiply the fan hours reported in the SS-L report by the DOAS fan power to see if the reported energy makes sense.
Regards,
~Bill