90.1-2007 fan power pressure drop allowance question

2 posts / 0 new
Last post

The 90.1-2007 fan pressure drop allowance includes credit for sound attenuation sections. Do you apply the credit for each silencer on a system? The system I am looking at has 3 silencers, one on the supply duct, one on each or two return ducts entering the AHU.

[Title: RWDI - Description: RWDI logo]

Christopher Jones, P.Eng. | Senior Energy Analyst
RWDI
901 King Street West, Suite 400, Toronto, ON M5V 3H5 Canada
Tel: (519) 823-1311 ext 2052
rwdi.com

________________________________
RWDI - A Platinum Member of Canada's 50 Best Managed Companies
This communication is intended for the sole use of the party to whom it was addressed and may contain information that is privileged and/or confidential. Any other distribution, copying or disclosure is strictly prohibited. If you received this email in error, please notify us immediately by replying to this email and delete the message without retaining any hard or electronic copies of same. Outgoing emails are scanned for viruses, but no warranty is made to their absence in this email or attachments. If you require any information supplied by RWDI in a different format to facilitate accessibility, contact the sender of the email, email solutions at rwdi.com or call +1.519.823.1311.

Bldg simulation's picture
Offline
Joined: 2016-04-13
Reputation: 400

Dear Chris,
I have made the assumption that the pressure drop imposed by the silencers *on
the fan system* is the value that should be counted.

3 silencers on the supply side, for example, only affect the fan the same
as one silencer (assuming they're in parallel). If, as you say, there is
also one on the return side, then both will affect the fan and both should
be counted.