Core and Shell Office Buildings: Do you model conference rooms

3 posts / 0 new
Last post

Hi Nick,

We?ve used 10% as a standard proportion for meeting/conference spaces in a C&S office for LEED previously with no issues. We?ve had comments specifically targeting this as a requirement for 62.1 calculations in C&S buildings when you have a multi-zone VAV system ? or any other system where the fresh air is a variable proportion of the conditioned air. We produced a notional floor plan suggesting how it could be zoned, although the level of detail used was minimal. This seems sensible given that the building upon fit-out will have a variety of space types, which will usually follow a relatively predictable layout and the design should be capable of coping with this.

Hope that helps,

Edwin Wealend
Principal Engineer
Cundall Engineering Design Consulting (Shanghai) co., Ltd
????????????????
T +86 021 5836 6138
F +86 021 5836 6137
www.cundall.com.cn

[cid:image005.png at 01CFFF25.126BC800] [cid:image006.png at 01CFFF25.126BC800]
Suite 2102, 21/F, Longyu Tower, 1036 South Pudong Road, Pudong, Shanghai, 200120, P.R.China
???????????1036?????2102? ??: 200120

Please consider the environment before printing this e-mail

Wealend, Edwin's picture
Offline
Joined: 2013-02-18
Reputation: 0