ASHRAE 90.1G Exhaust Fan modeling problems

4 posts / 0 new
Last post

Dear All,

I got two questions about exhaust fan modeling according to ASHRAE 90.1G-2010, clarifications from experience people would be great;

1- Proposed system has an exhaust fan, hence I`ll model exhaust fan for 7. VAV with Reheat system as well.

G3.1.2.9.1 says that I should model exhaust fan size as 90% of supply fan. Fair enough, peak flow rate from exhaust will be 90% of VAV peak supply, so there is positive pressure in baseline design zones.

Further, G3.1.2.10.1 says that peak fan power should be split between supply and exhaust in the same proportion as proposed design. For example, my proposed design got 1000 CFM for supply and 1000 CFM for exhaust, so I`ll split "Peak Fan Power Consumption" 50% on baseline design as well.

Finally I`ll model VAV Supply Fan curve as mentioned in G3.1.3.15.

However, here is my real question: What about efficiency curve of the exhaust fan? Appendix G doesn`t say anything about this issue. It only says that (G3.1.2.1) efficiency of HVAC equipment should be modeled as minimum as shown on section 6.4. Section 6.4 doesn`t say anything about Exhaust Fans.

So that means I can arrange efficiency curve of the exhaust fan in baseline however I want? This kinda opens up the possibility of gaming the system, one can see where exhaust fan will usually work and set the efficiency very low at that point of the curve, hence higher kWh consumption for the baseline system.

Could someone experience clarify what should be the efficiency curve of Exhaust Fans according to ASHRAE 90.1G 2010 edition?

2- As far as I understood, ASHRAE 90.1G says that exhaust fans shouldn`t be modeled for spaces where no supply fan exists. Or better put, if HVAC system serving the zone has no supply fan, then you cannot model exhaust fan.

This seems extremely unfair for large scale projects where garage exhaust fans, toilet exhaust fans are considerably large.

Has any of you tried to model garage and toilet fans in your baseline model and pass through LEED review? What is the best way to follow if your proposed system got garage exhaust and toilet exhaust fans? I really want to model those in baseline as well because it will affect my energy efficiency rating.

Kind regards,

Ismail Volkan Ozdemir
Mechanical Engineer, LEED AP BD+C

________________________________

The information contained in this e-mail (including any attachments) is confidential.
It must not be disclosed to any person without written authority of Renaissance Construction Ltd.
If you are not the intended recipient, please delete it from your system immediately

www.rencons.com

Volkan Ozdemir's picture
Offline
Joined: 2015-05-19
Reputation: 0

Hi Volkan,
I can answer your second question. Exhaust fans in unconditioned zones should be modeled identical in base and proposed case.
Regards,Rathnashree

Dear All, ? I got two questions about exhaust fan modeling according to ASHRAE 90.1G-2010, clarifications from experience people would be great; ? 1-?????Proposed system has an exhaust fan, hence I`ll model exhaust fan for 7. VAV with Reheat system as well. G3.1.2.9.1 says that I should model exhaust fan size as 90% of supply fan. Fair enough, peak flow rate from exhaust will be 90% of VAV peak supply, so there is positive pressure in baseline design zones. ? Further, G3.1.2.10.1 says that peak fan power should be split between supply and exhaust in the same proportion as proposed design. For example, my proposed design got 1000 CFM for supply and 1000 CFM for exhaust, so I`ll split ?Peak Fan Power Consumption? 50% on baseline design as well. Finally I`ll model VAV Supply Fan curve as mentioned in G3.1.3.15. ? However, here is my real question: What about efficiency curve of the exhaust fan? Appendix G doesn`t say anything about this issue. It only says that (G3.1.2.1) efficiency of HVAC equipment should be modeled as minimum as shown on section 6.4. Section 6.4 doesn`t say anything about Exhaust Fans. ? So that means I can arrange efficiency curve of the exhaust fan in baseline however I want? This kinda opens up the possibility of gaming the system, one can see where exhaust fan will usually work and set the efficiency very low at that point of the curve, hence higher kWh consumption for the baseline system. ? Could someone experience clarify what should be the efficiency curve of Exhaust Fans according to ASHRAE 90.1G 2010 edition? ? 2-??????As far as I understood, ASHRAE 90.1G says that exhaust fans shouldn`t be modeled for spaces where no supply fan exists. Or better put, if HVAC system serving the zone has no supply fan, then you cannot model exhaust fan. This seems extremely unfair for large scale projects where garage exhaust fans, toilet exhaust fans are considerably large. Has any of you tried to model garage and toilet fans in your baseline model and pass through LEED review? What is the best way to follow if your proposed system got garage exhaust and toilet exhaust fans? I really want to model those in baseline as well because it will affect my energy efficiency rating. ? Kind regards, ?
| Ismail Volkan Ozdemir Mechanical Engineer, LEED AP BD+C |

? ?

The information contained in this e-mail (including any attachments) is confidential.
It must not be disclosed to any person without written authority of Renaissance Construction Ltd.
If you are not the intended recipient, please delete it from your system immediately

www.rencons.com

_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send? a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG

Rathna Shree's picture
Offline
Joined: 2011-10-02
Reputation: 0

A few thoughts:

- Distributing power between baseline fans in proportion to the
proposed should probably reference proposed fan powers, not flows

- If you are going to have your exhaust fan operate on VSD and
track the supply, then intuitively the only VSD fan curve provided by 90.1
is as cited under 3.1.3.15, and I would use the same for each system fan.
I should think you could also logically specify a distinct system exhaust
operation/flow schedule citing & matching the proposed design.

- A general caution on ?gaming? the system: There are a myriad of
subtle, clever, and diabolical ways one could subvert the intent/purpose of
Appendix G and its ilk? but then what?s the point? Bruce Lee comes to
mind: ?Obey the principles without being bound by them.? It?s never a
good feeling to look back on a bunch of hours you?ve invested developing a
simulation that doesn?t really represent anything.

- #2: I think you are trying to read new meanings into
G3.1.2.9.1?? Generally for LEED projects, I routinely handle garage
ventilation, local/centralized restroom exhaust, and similar standalone
ventilation systems operating independently of space conditioning systems
as ?process? ventilation (indicating the associated energy consumptions as
such on the EAp2 template). Essentially those exhaust/ventilation systems
are defined in the proposed model as actually occurring, then the baseline
model is made to match the proposed case. I?ll often include additional
sub-metering (eQuest) so that I can further demonstrate/document the claim
they?ve been made to match at submission.

Hope that helps!

~Nick

*NICK CATON, P.E.*
*Owner*

*Caton Energy Consulting*
1150 N. 192nd St., #4-202

Shoreline, WA 98133
office: 785.410.3317

www.catonenergy.com

*From:* Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] *On Behalf
Of *Rathna Shree
*Sent:* Wednesday, May 20, 2015 12:12 AM
*To:* Volkan Ozdemir; bldg-sim at lists.onebuilding.org
*Subject:* Re: [Bldg-sim] ASHRAE 90.1G Exhaust Fan modeling problems

Hi Volkan,

I can answer your second question. Exhaust fans in unconditioned zones
should be modeled identical in base and proposed case.

Regards,

Rathnashree

On Monday, 18 May 2015 6:22 PM, Volkan Ozdemir
wrote:

Dear All,

I got two questions about exhaust fan modeling according to ASHRAE
90.1G-2010, clarifications from experience people would be great;

1- Proposed system has an exhaust fan, hence I`ll model exhaust fan
for 7. VAV with Reheat system as well.

G3.1.2.9.1 says that I should model exhaust fan size as 90% of supply fan.
Fair enough, peak flow rate from exhaust will be 90% of VAV peak supply, so
there is positive pressure in baseline design zones.

Further, G3.1.2.10.1 says that peak fan power should be split between
supply and exhaust in the same proportion as proposed design. For example,
my proposed design got 1000 CFM for supply and 1000 CFM for exhaust, so
I`ll split ?Peak Fan Power Consumption? 50% on baseline design as well.

Finally I`ll model VAV *Supply* Fan curve as mentioned in G3.1.3.15.

However, here is my real question: What about efficiency curve of the
exhaust fan? Appendix G doesn`t say anything about this issue. It only says
that (G3.1.2.1) efficiency of HVAC equipment should be modeled as minimum
as shown on section 6.4. Section 6.4 doesn`t say anything about Exhaust
Fans.

So that means I can arrange efficiency curve of the exhaust fan in baseline
however I want? This kinda opens up the possibility of gaming the system,
one can see where exhaust fan will usually work and set the efficiency very
low at that point of the curve, hence higher kWh consumption for the
baseline system.

Could someone experience clarify what should be the efficiency curve of
Exhaust Fans according to ASHRAE 90.1G 2010 edition?

2- As far as I understood, ASHRAE 90.1G says that exhaust fans
shouldn`t be modeled for spaces where no supply fan exists. Or better put,
if HVAC system serving the zone has no supply fan, then you cannot model
exhaust fan.

This seems extremely unfair for large scale projects where garage exhaust
fans, toilet exhaust fans are considerably large.

Has any of you tried to model garage and toilet fans in your baseline model
and pass through LEED review? What is the best way to follow if your
proposed system got garage exhaust and toilet exhaust fans? I really want
to model those in baseline as well because it will affect my energy
efficiency rating.

Kind regards,

*Ismail Volkan Ozdemir*

*Mechanical Engineer, LEED AP BD+C*

------------------------------

The information contained in this e-mail (including any attachments) is
confidential.
It must not be disclosed to any person without written authority of
Renaissance Construction Ltd.
If you are not the intended recipient, please delete it from your system
immediately

www.rencons.com

_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG

Nicholas Caton's picture
Offline
Joined: 2014-12-09
Reputation: 0

Hi Chris!

I generally draw a line where a fan is involved with space conditioning.
If we?re talking about restroom fans operating independently from the air
handlers, I?d be comfy calling that ?process,? but if we?re talking about a
kitchen?s MAU or heat recovery exhaust fans, that wouldn?t get copied over
to the baseline.

Pfan definitely is supposed to incorporate all fans associated with the
baseline system. No questions there. This line is probably informed in
part where GBCI has made it clear garage ventilation is an example of a
process load. The ?space conditioning? litmus is how I reconcile that
example with the Pfan rules.

To date, I?ve not had issue with this approach in term of LEED review, and
I?m quite clear in documenting these distinctions. As always however,
YMMV!

[Chris separately okayed me sending this reply to the list, by the way.]

~Nick

*NICK CATON, P.E.*
*Owner*

*Caton Energy Consulting*
1150 N. 192nd St., #4-202

Shoreline, WA 98133
office: 785.410.3317

www.catonenergy.com

*From:* Jones, Christopher [mailto:cjones at halsall.com ]
*Sent:* Wednesday, May 20, 2015 4:59 AM
*To:* Nicholas Caton
*Subject:* RE: [Bldg-sim] ASHRAE 90.1G Exhaust Fan modeling problems

Hello Nick,

I am wondering about your approach to treat exhaust fans as ?process?. I
thought the System Fan power was to be calculated including all supply,
return, exhaust and relief fans on the system. I have been interpreting
that (G3.1.2.9.2) to mean that washroom, storage room, and other exhaust
fans receiving make-up air from the System are included in the fan power
calculation for that System. If the Proposed design fan power is greater
than the allowance, then I reduce all the fans (including the exhaust fans)
in the Baseline model proportionally.

*Christopher Jones**,* P.Eng.
Tel: 416.644.4226 ? Toll Free: 1.888.425.7255 x 527

*From:* Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org
] *On Behalf Of *Nicholas Caton
*Sent:* Wednesday, May 20, 2015 7:20 AM
*To:* Rathna Shree; Volkan Ozdemir; bldg-sim at lists.onebuilding.org
*Subject:* Re: [Bldg-sim] ASHRAE 90.1G Exhaust Fan modeling problems

A few thoughts:

- Distributing power between baseline fans in proportion to the
proposed should probably reference proposed fan powers, not flows

- If you are going to have your exhaust fan operate on VSD and
track the supply, then intuitively the only VSD fan curve provided by 90.1
is as cited under 3.1.3.15, and I would use the same for each system fan.
I should think you could also logically specify a distinct system exhaust
operation/flow schedule citing & matching the proposed design.

- A general caution on ?gaming? the system: There are a myriad of
subtle, clever, and diabolical ways one could subvert the intent/purpose of
Appendix G and its ilk? but then what?s the point? Bruce Lee comes to
mind: ?Obey the principles without being bound by them.? It?s never a
good feeling to look back on a bunch of hours you?ve invested developing a
simulation that doesn?t really represent anything.

- #2: I think you are trying to read new meanings into
G3.1.2.9.1?? Generally for LEED projects, I routinely handle garage
ventilation, local/centralized restroom exhaust, and similar standalone
ventilation systems operating independently of space conditioning systems
as ?process? ventilation (indicating the associated energy consumptions as
such on the EAp2 template). Essentially those exhaust/ventilation systems
are defined in the proposed model as actually occurring, then the baseline
model is made to match the proposed case. I?ll often include additional
sub-metering (eQuest) so that I can further demonstrate/document the claim
they?ve been made to match at submission.

Hope that helps!

~Nick

*NICK CATON, P.E.*
*Owner*

*Caton Energy Consulting*
1150 N. 192nd St., #4-202

Shoreline, WA 98133
office: 785.410.3317

www.catonenergy.com

*From:* Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] *On Behalf
Of *Rathna Shree
*Sent:* Wednesday, May 20, 2015 12:12 AM
*To:* Volkan Ozdemir; bldg-sim at lists.onebuilding.org
*Subject:* Re: [Bldg-sim] ASHRAE 90.1G Exhaust Fan modeling problems

Hi Volkan,

I can answer your second question. Exhaust fans in unconditioned zones
should be modeled identical in base and proposed case.

Regards,

Rathnashree

On Monday, 18 May 2015 6:22 PM, Volkan Ozdemir
wrote:

Dear All,

I got two questions about exhaust fan modeling according to ASHRAE
90.1G-2010, clarifications from experience people would be great;

1- Proposed system has an exhaust fan, hence I`ll model exhaust fan
for 7. VAV with Reheat system as well.

G3.1.2.9.1 says that I should model exhaust fan size as 90% of supply fan.
Fair enough, peak flow rate from exhaust will be 90% of VAV peak supply, so
there is positive pressure in baseline design zones.

Further, G3.1.2.10.1 says that peak fan power should be split between
supply and exhaust in the same proportion as proposed design. For example,
my proposed design got 1000 CFM for supply and 1000 CFM for exhaust, so
I`ll split ?Peak Fan Power Consumption? 50% on baseline design as well.

Finally I`ll model VAV *Supply* Fan curve as mentioned in G3.1.3.15.

However, here is my real question: What about efficiency curve of the
exhaust fan? Appendix G doesn`t say anything about this issue. It only says
that (G3.1.2.1) efficiency of HVAC equipment should be modeled as minimum
as shown on section 6.4. Section 6.4 doesn`t say anything about Exhaust
Fans.

So that means I can arrange efficiency curve of the exhaust fan in baseline
however I want? This kinda opens up the possibility of gaming the system,
one can see where exhaust fan will usually work and set the efficiency very
low at that point of the curve, hence higher kWh consumption for the
baseline system.

Could someone experience clarify what should be the efficiency curve of
Exhaust Fans according to ASHRAE 90.1G 2010 edition?

2- As far as I understood, ASHRAE 90.1G says that exhaust fans
shouldn`t be modeled for spaces where no supply fan exists. Or better put,
if HVAC system serving the zone has no supply fan, then you cannot model
exhaust fan.

This seems extremely unfair for large scale projects where garage exhaust
fans, toilet exhaust fans are considerably large.

Has any of you tried to model garage and toilet fans in your baseline model
and pass through LEED review? What is the best way to follow if your
proposed system got garage exhaust and toilet exhaust fans? I really want
to model those in baseline as well because it will affect my energy
efficiency rating.

Kind regards,

*Ismail Volkan Ozdemir*

*Mechanical Engineer, LEED AP BD+C*

------------------------------

The information contained in this e-mail (including any attachments) is
confidential.
It must not be disclosed to any person without written authority of
Renaissance Construction Ltd.
If you are not the intended recipient, please delete it from your system
immediately

www.rencons.com

_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
------------------------------

You are receiving this communication because you are listed as a current
Parsons Brinckerhoff Halsall Inc. contact. Should you have any questions
regarding Parsons Brinckerhoff Halsall?s electronic communications policy,
please consult our Anti-Spam Commitment
or contact us at
caslcompliance at halsall.com.

CONFIDENTIALITY WARNING
This message is intended only for the use of the individual or entity to
which it is addressed, and may contain information which is privileged,
confidential, proprietary or exempt from disclosure under applicable law.
If you are not the intended recipient or the person responsible for
delivering the message to the intended recipient, you are strictly
prohibited from disclosing, distributing, copying or in any way using this
message. If you have received this communication in error, please notify
the sender, and destroy and delete any copies you may have received.

Nicholas Caton's picture
Offline
Joined: 2014-12-09
Reputation: 0