ASHRAE 90.1 - G3.1.2.8 Design Airflow Rates

2 posts / 0 new
Last post

Dear all,

I am modeling this same school for LEED 2009 purposes.

ASHRAE 90.1-2007 section "G3.1.2.8 Design Airflow Rates" states that System design supply airflow rates for the baseline building design shall be based on a supply-air-to-room-air temperature difference of 11?C or the required ventilation air or makeup air, whichever is greater.

Can someone please check the attached print screen and confirm if this is what they mean by supply air to room air temp difference?

Furthermore, if I leave the "Supply air flow rate" input for each zones as default in the baseline (instead of entering the supply CFM as in the proposed), I am getting a total consumption for the baseline to be less than the proposed! I am certainly not going to let eQUEST estimate the supply flow rates! Remember that I'm modeling for LEED and I aim for a 15% percent reduction in energy costs, which was a number I got when I assumed the baseline and proposed cases to have the same defined supply flow rates as per the ventilation rate procedure (provided to me by the design team).

Thanks for your help!

Omar Katanani

Omar Katanani's picture
Offline
Joined: 2011-09-30
Reputation: 0