ASHRAE 90.1 ERV 50% energy recovery effectiveness - eQUEST inputs?

6 posts / 0 new
Last post

I'd appreciate some sensible guidance. Please don't dampen my spirits...

Section 6.5.6.1 describes that required energy recovery systems (ERVs) "shall have at least 50% energy recovery effectiveness", meaning "a change in enthalpy of the outdoor air supply equal to 50% of the difference between the outdoor air and return air enthalpies at design conditions".
My reaction is to model this by setting both the sensible and latent effectiveness (ERV-SENSIBLE-EFF and ERV-LATENT-EFF) to 50% (0.50).
Is this correct?

Ye be thanked,
~Bill

William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer

[cid:image007.jpg at 01D2CFD5.C3882970] [cid:image008.jpg at 01D2CFD5.C3882970]

134 South Fitzhugh Street Rochester, NY 14608

T: (585) 698-1956 F: (585) 325-6005

bbishop at pathfinder-ea.com www.pathfinder-ea.com

[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.

via Equest-users's picture
Joined: 2016-07-15
Reputation: 400