The project is to demonstrate compliance using Section 11 of 90.1-2010. The proposed building has air-cooled heat recovery chillers that become air-to-water heat pumps when there is no cooling demand. The plant has natural gas boilers for the coldest days and to bring the DHW temperature up when the heat recovery chillers don?t product high enough temperatures. The HVAC systems are hydronically heated and cooled.
Is the Condenser Cooling Source Air/None? Or as most of the rejected heat goes into the heating loop side, is the condenser Water/Ground?
Then 11.3.2.j.2 indicates that the systems that use the secondary heating source type shall be modelled identically in the budget case and the primary heating source shall be used to determine the budget system type.
What does ?identically? mean ? that the heating plant shall be identical?
For example, if one assumes Air/None as the condenser source, then the single zone systems would be System 11, rooftop air conditioner with fossil fuel furnace. The multi-zone systems would be System 4, packaged rooftop VAV with reheat, hot water fossil fuel boiler. But if they budget systems are to be ?identical? would the heating plant in the budget case also be heat recovery chillers/heat pumps and boilers?
I am confused.
Christopher Jones, P.Eng.
Tel: 416.644.4226 ? Toll Free: 1.888.425.7255 x 527
______________________________________________________________________
NOTICE: This communication and any attachments ("this message") may contain confidential information for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on this message is strictly prohibited. If you have received this message in error, or you are not an authorized recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies.