Using Temperature Difference to Set Supply Airflows in Equest

1 post / 0 new

Hello-

I've been trying to get Equest to size supply airflows based on a 20 degree temperature difference (per ASHRAE 90.1) for baseline PSZ systems. Setting the Indoor Design Temperature (DESIGN-COOL-T) and Zone Entering Min Supply Temperature (MIN-SUPPLY-T) to get the temperature difference does not seem to work. Supply airflows are much too low (0.20 cfm/sf in many cases). I've checked other variables to ensure that nothing else is causing these low airflows.

The only other method I know of is to go outside Equest (into the INP file) and manually enter the SIZING-METHOD variable and set it to FLOW/CAPACITY (forcing Equest to use default cooling capacity to size supply airflow) and then manually enter MAX FLOW/CAPACITY and MIN/FLOW/CAPACITY (max and min cfm/ton) to get the desired temperature difference (for 20 degree temperature difference, 545 cfm/ton). Has anyone else had luck with this method or is there another suitable method out there?

Thanks!
Jeremy