Sandeep,
I would not recommend equating one cell and one battery because some
of the Type47 parameters are designed to limit voltage and current per
cell. A cell in a lead acid battery is about 2.1V. If you are
considering a system that uses 12V batteries then there are about 6
cells in series per battery. Assuming that these are 12V (6 cells in
series) batteries then to have 11 batteries in series would mean that
you've got 66 cells in series and 2 cells in parallel.
kind regards,
David

--
***************************