Good Afternoon,
I am trying to model a proposed geothermal system, however the end annual kWh usage in eQuest comes out to be around 25% of the quoted annual kWh usage from the engineer. What am I missing?
This is a building with 4 HVAC zones, each will be served by a waterfurnace system, and there is a ground loop with 2 pumps. The GSHP specs are directly from the geothermal engineer (below and also attached)
I'm also getting some warnings that I'm not sure how to resolve:
1. for each of the 4 systems, " A HEATING-CAPACITY of -29600. is inconsistent with a COOLING-CAPACITY of 38400. in SYSTEM EL1 Sys1 (PVVT) (G.SSE1)
Note: I am using the system sizing that the geothermal engineer forwarded
2. WLHP alarm limits
GSHP Plant Equipment
WS 1 of 2
Water Loop Properties
GSHP Loop: Head: 51 (This is lower, but the lowest equest allows is 51) Design DT: 10 F (a)
Pump Config: Single Loop Pump(s) only Loop Pumps-- Number: 2
Loop Flow: Variable Head/Flow: 23 ft 50gpm
Operation: Demand Setpoint: Fixed Motor Efficiency: Premium
Loop Temp Min: 33F Max: 75F Pump Control: Two Speed
WS 2 of 2
Ground Loop Heat Exchanger Properties
GHX Type: Vertical Well Field Pipe Size: 1 ½” Rating: Specify
Inner: 1.325” Outer: 1.9”
Configuration: Line of 4 U-Tube Leg Separation: 1”
Num of Identical Well Fields: 1 GHX Pipe Head: 30 ft
Depth: 500 ft Spacing: 20 ft Fluid Properties:
Borehole Diameter: 6” Fluid: Methanol
Pipe Material: Polyethylene Antifreeze Concern: 12%
Soil Thermal Properties and History
All settings left to default