You can designate the radiative/convective split of the heat gains from lighting using the LIGHT-RAD-FRAC keyword, the value for which can be accessed via the Space -> Lighting tab.
While there are (currently) no such input options for heat gains from Equipment and Internal Energy Sources, the keywords exist in DOE-2.2 and can be used in the input files for your eQUEST models.
For example, you can satisfy the requirement in PNNL's PRM Reference Manual
EQUIP-RAD-FRAC = (
{if (#L("FLOOR-WEIGHT") > 0. .or. #RV(#L("EQUIP-SCHEDULE",0)) !=0)
then unused
else 0.20 /* Per PNNL-25130 90.1-2010 PRM Reference Manual */
endif} )
The SOURCE-RAD-FRAC keyword is also available, for describing the heat gains from Internal Energy Sources.
Cheers,
~Bill
[cid:image002.png at 01D1BB58.F3BF4610]
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image004.jpg at 01D1BB58.F3BF4610] [cid:image006.jpg at 01D1BB58.F3BF4610]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.