Hi Guys,
I am trying to model nigh pre-cooling in E-quest. I was looking through
Archives but was unable to solve the problem. I have attached pd2 and inp
file for the project. Basically every thing is default from E-quest except
following items:
Detail Data Edit: E-quest 3.63
Building Shell Components:
1) Screen1: Office Building High Rise
2) Screen3: Roof 4-inc concrete with R-18 Insulation/ Wall 10-inch Concrete
no insulation
3) Screen12: Operating Schedule: Typical Use: 8.00 AM to 10.00 PM (MF), SUN,
SAT, Holiday Closed
Air-Side System Types:
HVAC System 1:
1) Screen1: Dual Duct System (chilled water/ hot water coil)
2) Screen2: E-quest Default Values
3) Screen4: Fan Type: Forward Curved Centrifugal
4) Screen5: Fan Schedule: Fan Operates 5-hours before and 1-hour building
occupancy schedule. This is what currently implemented at the site. Fans are
run 5-hours before occupancy in order to pre-cool building and use thermal
mass of the building.
5) Screen6: E-Quest Default Economizer 70F
6) Screen7: OA reset on Hot and Cold Deck.
Now my question is if I simulate this model and see hourly report I see
cooling load at 3.00 AM in the morning. I know my fan scheduled to run from
3.00 AM to 11.00 PM, but why it's using chilled water when it's cold
outside. If I simply match fan schedule to building occupancy schedule I see
savings on both chilled and hot water use.
Also if set Night Cycle Control in Detail Data edit to Night Vent Schedule
(When Scheduled) with new ON/off Schedule (from 3.00 AM to 11.00 PM), Night
Vent Delta T = 5F, my energy consumption is lower than running fans from
3.00 AM to 11.00 PM without night vent but still higher than running fans
from 8.00AM to 10.00PM. I am not getting any credit for thermal mass and
pre-cooling, unless I am modeling incorrectly. Any help is appreciated.
Thank you.
Regards,
Amol Mehta