New eQuest VRF capabilities - Questions - custom BDLDialogs.txt file

2 posts / 0 new
Last post

Hey Nick,
I couldn't find MAX-CAP/UNIT in the interface and I believe it was just overlooked. You can modify the necessary file to include it as follows:

* Find the BDLDialogs.txt file in Documents -> eQUEST 3-65-7175 Data -> ScreensDOE23
* Save a backup copy of the file with a different name.
* Edit the BDLDialogs.txt file:
* Using a text editor, search for: LABEL, "Rated and Design Conditions - Cooling"
* Insert the following lines of text immediately preceding the LABEL line:
; WJB 11/09/18 - added new input field
EDIT, 19460, 19460, 0, 1, SYSTEM, 0, MAX-CAP/UNIT, 0, STD, 580, 55, 23, 70, 0, 3, "Max Capacity per Unit:", LEFT, -145, 5, 1, LEFT, 4, 5,"Maximum size per indoor unit. Used for modeling of branch refrigerant piping. Affects thermal and friction losses."

* Save the BDLDialogs.txt file.
* Run eQUEST as you normally would.

Your VRF Coil tabpage should now look like this:
[cid:image002.png at 01D4785B.F54E1840]

I believe your understanding of NUM-OF-UNITS is correct.

~Bill

William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer

[Pathfinder-EA-logo-2]T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com www.pathfinder-ea.com