The narrative response indicates that the Baseline boiler has been modeled utilizing operating performance curves and a boiler HIR of 1.25. However, since the boiler operation HIR is based on the performance curves, the HIR is less than 1.25 in the part-load condition, which is inappropriate. Revise the Baseline boilers to include a flat efficiency of 80% for all part-loads. Provide eQuest input files or screen shots verifying the boiler efficiency has been modeled as required.
However, I can not understand it very much. The minimum equipment efficiency requirement(80 % Et) of Ashrae 90.1-2007 should be base on full load condition.Why the LEED reviewer raise such a question?Any insight is appreciate!!