I am trying to sift through how eQuest calculates a chiller's end
electrical usage and I am stuck on the fraction of hour the chiller
operates.
The DOE-2 engineers manual says it is calculated as follows:
FRAC = PL / RMIN,
where PL is the average part load ratio over the hour, calculated as:
PL = ALOAD / CAP,
where ALOAD is the assigned hourly load and CAP is the corrected
operating capacity.
RMIN is the part load ratio of rated load at which the chiller can
operate continuously.
I have used some of the calculated values in the hourly report and
cannot verify how eQuest is calculating this FRAC amount.
Does anyone have some insight?
Thanks,
Aaron Etzkorn, EIT