Fan Power

10 posts / 0 new
Last post

This is a DOE-2 question, I think, but I am applying it to EnergyPro. I
am asking here in the hopes that some will have a more in-depth
knowledge of DOE-2 and how it relates to fan power. I am also hoping
that some here will be able to reflect on the theory and application of
fan power and energy as it relates to actual systems and modeling.

When inputting indoor fan power, I have used many sources for the fan
power. I sometimes use the motor nameplate, which I believe is too high
in every case.

I also sometimes use FLA or RLA, which I also do not believe are
accurate, but sometimes give more realistic numbers.

Some manufacturers give fan BHP at design conditions, which I find to be
very helpful, but not everybody is that helpful.

It has been suggested that I calculate the fan BHP using the theoretical
formula *** Fan BHP = (cfm x static press "w.c.) / (6356 x fan
efficiency) *** and then use a conservative fan efficiency (maybe 50%)
for a good number. This gives a much lower value than the other
methods, and I am trying to see if there is anything wrong with this
approach.

As I understand the usage, indoor fan power is divided by motor and
drive efficiency to come up with fan energy. So the fan BHP is the
starting point. Having this too high drives up fan energy, sometimes
dramatically, and can influence the proposed case quite a bit if there
are lots of fans, even small fans.

Any thoughts on this approach would be very much appreciated.

--