Hello,I have a model in eQUEST that has FCU as the HVAC system with heat pump chiller for a residential building.?Now I need to change this HVAC system to DX heat pump and this heat pump is small and self contained in which it can be installed inside the room and will have inlet and out let ducts for the condenser air to the outside (I.e. without outdoor unit). This unit will have also heat recovery option and supplementary electric resistance heater.My question is, what is the best HVAC system in eQUEST that I can use for this heat pump and in the same time enable the heat recovery option tab and the supplementary heater option tab? And also, do I need to assign a new HVAC system for each zone or I can assign one HVAC system for a group of zones similar to the FCU system?Thank you very much for the help.RegardsAhmad

Ahmad Fraij's picture
Offline
Joined: 2020-10-13
Reputation: 0

Ahmed:
When you change systems, you will definitely need a new run. And you describe the DX heat pump as self contained. I will assume this is a room size heat pump, such as a thru wall unit in a hotel.
What you would use heat recovery for (not sure the DX unit can do that) is beyond me.
John R Aulbach, PE
On Sunday, September 3, 2023 at 09:35:38 PM PDT, fraij via Equest-users wrote:

Hello,
I have a model in eQUEST that has FCU as the HVAC system with heat pump chiller for a residential building.?
Now I need to change this HVAC system to DX heat pump and this heat pump is small and self contained in which it can be installed inside the room and will have inlet and out let ducts for the condenser air to the outside (I.e. without outdoor unit). This unit will have also heat recovery option and supplementary electric resistance heater.
My question is, what is the best HVAC system in eQUEST that I can use for this heat pump and in the same time enable the heat recovery option tab and the supplementary heater option tab? And also, do I need to assign a new HVAC system for each zone or I can assign one HVAC system for a group of zones similar to the FCU system?
Thank you very much for the help.
Regards
Ahmad

_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send? a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

John Aulbach's picture
Offline
Joined: 2011-09-30
Reputation: 1

You have a couple of options regarding system type. There is a HP heat pump system type that is zonal meaning you would not need a system per zone.?? However it has some keyword limitations including no ventilation heat recovery.?? So to work around model heat recovery you will scale back the OA volume by the heat recovery effectiveness.?? ( Not terrific. )

I recommend creating a system per zone and using the PVVT system type. PSZ would also work.? PVVT enables a few more keywords.?? Both allow ventilation heat recovery to be directly modelled.

Whichever system you choose, set your heating to Heat Pump.?? The keywords on the heating-supplementary tab will be enabled where you can add the OAT below which your electric resistance heating is enabled (default 40F) and the OAT below which the heat pump doesn't run.

bfountain's picture
Offline
Joined: 2011-09-30
Reputation: 201

Hello Ahmad:

When considering air-source heat pumps you also need to carefully in cold climates to watch for large peak heating demand since the heat pump simulation in PSZ will switch-over to electric resistance heating as temperatures below apx. 30F. This results in a large jump in electric demand as the unit cannot maintain space temperatures at outdoor temperatures below 30F.

This was one of the reasons for the large, unexpected load on the grid during the winter storm a few years back because of the large number of Texas residences with air to air heat pumps.

Avoiding this is possible with a ground heat exchanger for the heat pump (if this is possible on the site).

Also, several manufacturers are solving this with new technologies that allow the heat pump to continue to provide heat in cold climate conditions. However, defining these new HP systems in DOE-2, Equest or EP+ requires some work with adjusting the equipment parameters.

Jeff

Jeff S. Haberl, Ph.D., P.E.inactive, FASHRAE, FIBPSA We are like fluttering leaves on the branches of trees

Liz & Nelson Mitchell Professor in Residential Design in the forest of the landscape that surrounds us.

Department of Architecture If we could, for just a moment, flutter together,

Texas A&M University we could lift the earth up to be a better place. JSH 2022

College Station, TX 77845-3581

Office: 979-845-6507, Lab: 979-845-6065

Fax 979-862-2457

jhaberl at tamu.edu,www.esl.tamu.edu

Jeff Haberl2's picture
Offline
Joined: 2011-10-02
Reputation: 200