I think I found a bug with the ERV feature in eQuest related to
temperature control. My input is as follows:
RECOVER-EXHAUST = YES
ERV-RECOVER-TYPE = ENTHALPY-WHEEL
ERV-SENSIBLE-EFF = 0.75
ERV-LATENT-EFF = 0.75
ERV-RUN-CTRL = OA-EXHAUST-DT
ERV-TEMP-CTRL = MIXED-AIR-RESET
ERV-CAP-CTRL = MODULATE-HX
ERV-HX-KW = 0.207
ERV-FANS = HVAC-SUPPLY/RETURN
ERV-OA-STATIC = 0.5
ERV-EXH-STATIC = 0.5
ERV-FROST-CTRL = USE-CAP-CTRL
The system shows heating savings as expected, and cooling savings during
summer periods, but during winter there is a large cooling penalty.
Hourly reports show an unexpected cooling load during winter night mode
operation. If I set ERV-OA-STATIC to zero, that cooling load goes away.
If I change to a fan located in the ERV, the unexpected cooling load is
still absent:
ERV-FANS = SELF-CONTAINED
ERV-EXH-KW/FLOW = 0.002
Thus, it appears that the heat gain due to friction in the heat wheel is
not taken into account for the OA setpoint during night mode when
ERV-FANS = HVAC-SUPPLY/RETURN. Has anyone else seen this problem?
The SELF-CONTAINED option appears to be a work-around, but it is not as
convenient for add-on heat wheels.
Thanks,
Doug Maddox, PE