The important thing to consider is that eQUEST?s definition of EER may not match the ARI-rated EER as the fan power and compressor power are usually separated in eQUEST whereas the fan power and compressor power are both included together in the ARI-ratings. This is where the more complicated conversions are coming from, as explained in detail in the RMI document linked by David.
All the best,
Daniel
?
Daniel Knapp PhD, P Phys, LEED AP
danielk at arborus.ca
Energy Efficiency Expert
Arborus Consulting
2-43 Eccles Street
Ottawa ON K1R 6S3
(613) 234-7178
Check out the link,
http://energy-models.com/forum/cooling-eir-and-unit-eer
Regards,
Siddharth
*Siddharth S. Patil*
Mechanical Engineer(MS)
Arizona State University,Tempe
Email: sspatil8 at asu.edu, patilsiddharth5 at gmail.com
Contact: +1 (480)-465-1540
Thanks Siddharth,
I did browse through this link but could not find the attachment that the
user had mentioned about.
I am looking for the source of the co-efficient; COOLING-EIR = (1/EER -
*0.012167*) / ((1 / 3.413) + *0.012167*)
Jayant, see if this helps ? search for ?EIR? and the section will come up:
http://www.rmi.org/Content/Files/EMITUsersGuide.pdf
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
Thanks David,
This document is helpful for my purpose of analysis.
Jay
Thank you Paul,
This is exactly what I was looking for. Spot on!!
Jay
EIR = 1 / COP
EIR = 3.412 / EER
EIR = (kW/ton) * (3.412/12)
Keith Swartz, PE | Senior Energy Engineer
Seventhwave
608.210.7123 seventhwave.org
Keith,
The important thing to consider is that eQUEST?s definition of EER may not match the ARI-rated EER as the fan power and compressor power are usually separated in eQUEST whereas the fan power and compressor power are both included together in the ARI-ratings. This is where the more complicated conversions are coming from, as explained in detail in the RMI document linked by David.
All the best,
Daniel
?
Daniel Knapp PhD, P Phys, LEED AP
danielk at arborus.ca
Energy Efficiency Expert
Arborus Consulting
2-43 Eccles Street
Ottawa ON K1R 6S3
(613) 234-7178
Good point, Daniel.
Keith Swartz, PE | Senior Energy Engineer
Seventhwave
608.210.7123 seventhwave.org