I recently changed the thermostat schedule and design air flow (to 1 cfm/ft?) for a bunch of zones on a VAV air handler. After saving this change and reloading the project, I get an error "TYPE NOT FIRST KEYWORD" for each zone I changed.
I'd understand this if each zone had its own system, but all these zones are assigned to the same VAV AHU. The system TYPE is defined at the top of the system definition as VAVS. A portion of the .inp file showing the system definition and the first error-causing zone is included below.
Any idea what might be causing this error? Any help is appreciated.
James D. Waechter, P.E., LEED A.P.
"E1 Sys1 (PVAVS) (B)" = SYSTEM
TYPE = VAVS
HEAT-SOURCE = HOT-WATER
HEAT-SIZING-RATI = 1.25
COOL-SIZING-RATI = 1.15
COOL-RESET-SCH = "AHU S.A. Temp Reset Schedule"
COOL-CONTROL = RESET
ECONO-LIMIT-T = 75
SUPPLY-KW/FLOW = 0.00062
RETURN-KW/FLOW = 0.00062
FAN-EIR-FPLR = "ForCurve w Dischrg Dampers FPLR"
REHEAT-DELTA-T = 50
HW-VALVE-TYPE = TWO-WAY
HW-LOOP = "Hot Water Loop"
CHW-LOOP = "Chilled Water Loop"
..
"E1 SE Perim ML Zn (ML.SE1)" = ZONE
FLOW/AREA = 1
MIN-FLOW/AREA = 0.4
HEAT-TEMP-SCH = "S1 Sys1 (PVAVS) Heat Sch"
DESIGN-COOL-T = 75
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
SPACE = "E1 SE Perim ML Spc (ML.SE1)"