Everyone, I have been modeling some dormitories with a proposed HVAC
system involving a DOA with a full exhaust air HX and MERV 13 filters.
The puzzle is what to do about the baseline PTAC fan power energy? If I
use 0.3 w/cfm as Appendix G suggests, my PTAC baseline system does not
account for a fully ducted return\exhaust or MERV 13 filters. The
commercial fan power equation for systems 3-8 accounts for this, but I
am not supposed to use that formula for System 1 and 2.
Another puzzle is if I develop an cooling EIR value for my baseline PTAC
using the 365 w/kCFM conversion rule and equate that with 0.3 w/cfm,
what happened to the other 65 w/kCFM?
Maybe ARI 310/380 doesn't use 365 w/cfm fan power? I read it and didn't
find any statement regarding fan power requirements, but I assume it
works the same as ARI 210/240?
I am wondering if a compromise of
PTAC fan power = CFMs *0.000365 + A
where A= PD*CFMs /4131 and PD = 1.4
might be a reasonable solution?
PTAC fan power = 0.00063 kw/cfm
Does anyone else have experience with this puzzle?
Kathryn Kerns