Hello,
With 90.1 2010, I wonder how to apply the fan power limitation pressure drop adjustment formula for an ERV:
(2.2 * Energy Recovery Effectiveness) - 0.5 in w.c. for each airstream
I don't find example in the 90.1 user's manual about ERV, does the "for each stream" statement apply to the "0.5 in w.c." or to the all formula ?
With a 10,000 cfm ventilation fan and a sensible wheel with a 60% efficiency, what would be the pressure drop adjustment for the ERV?
? 10,000 * ( (2.2 * 0.6 ) - 0.5 * 2) = 3,200 hp
Or
? 10,000 * 2 * ( (2.2 * 0.6 ) - 0.5)=16,400 hp
It's definitively not the same !
Thanks
Julien
Julien Dutel, ing., CEM, CMVP.
Direction des secteurs r?sidentiel, institutionnel et des affaires
Bureau de l'efficacit? et de l'innovation ?nerg?tiques
Minist?re des Ressources naturelles
5700, 4e Avenue Ouest, B-406
Qu?bec (Qu?bec) G1H 6R1
T?l?phone : 418 627-6379, poste 8060
T?l?phone sans frais : 1 877 727-6655
T?l?copieur : 418 643-5828
http://www.efficaciteenergetique.mrn.gouv.qc.ca
AVIS DE CONFIDENTIALIT?
Ce message est confidentiel. Il est ? l'usage exclusif du destinataire ci-dessus. Si vous n'?tes pas le destinataire vis? ou une personne autoris?e ? lui remettre cette communication, vous ?tes par la pr?sente avis? qu'il est express?ment interdit de le diffuser, de le distribuer, de le reproduire, d'en d?voiler la teneur ou de prendre quelque mesure fond?e sur l'information qui y est contenue. S'il vous a ?t? envoy? par erreur, veuillez en informer imm?diatement l'exp?diteur par t?l?phone au 418 627-6379 et d?truire ce message ainsi que toute copie de celui-ci.