Probably I'm missing something obvious... but is there no way to review/edit glass type assignment in detailed mode window properties? I've managed with creating expressions / reviewing / editing via the spreadsheet view but this has started bugging me as I keep catching myself looking for something I don't think is actually there...
[cid:image001.png at 01D29732.E7F99C20]
[cid:image002.png at 01D29732.E7F99C20]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image003.png at 01D29732.E7F99C20]
Nick,
I'm not sure why your specification method is blank. Do you have "no_def"
in the user expression? If you set the specification method to "composite"
a dialog box should appear under specification method that allows you to
select the type of glass.
Kevin McGaffigan, PE
DMI
300 Chestnut Street, Suite 150
Needham, MA 02492
781-449-5700 x12
That's the fix!
Huh - the doe2 default is "required" but I know I've seen this field empty for many different models without any obvious repercussions...
~Nick
[cid:image002.png at 01D2973F.CFBDEC30]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image003.png at 01D2973F.CFBDEC30]