VAV system unmet hours

5 posts / 0 new
Last post

I am modeling a system which consists of rooftop AHU's that serve
multiple VAV boxes in a classroom/office building. The AHU's are served
by chilled water and hot water loops for conditioning. The problem I am
having is that the systems are coming up in the SS-R report as having
large amounts of unmet hours. Even if I try to manually add heating to
the systems there is no affect on the hours. I have attached the pd2 and
inp files. Any suggestions would be appreciated. Thanks

Brett M. West

Brett M. West's picture
Offline
Joined: 2011-09-30
Reputation: 0

Wrong .inp file. send out the one without "- Baseline Design" after your file name

Timothy Howe, MS, LEED? AP

Howe, Timothy's picture
Offline
Joined: 2011-09-30
Reputation: 0

Sorry. Here is the correct inp file.

Brett M. West

Brett M. West's picture
Offline
Joined: 2011-09-30
Reputation: 0

Brett,

I think you might want to consider raising min. cfm in the rooms with
unmet heating load hours. Thanks!

Lan

Li, Lan's picture
Offline
Joined: 2011-09-30
Reputation: 0

What is your preheat coil design leaving air temp, right now you have it set to the default 45?F and with the reheat only providing a 30?F and the supply flow locked in your heating air temp can only be 75?F.

soooo... Q = CFM * 1.085 * Delta T

You have it so both the cfm and delta T are set, therefore your Q is limit to those parameters. You can either increase the preheat LAT so you get a greater delta T or remove the design CFM supply flow you have entered.

Timothy Howe, MS, LEED? AP

Howe, Timothy's picture
Offline
Joined: 2011-09-30
Reputation: 0