Dear users,
I manage to reduce the unmet hours at around 120, the problem is that the
majority of them are in the same zone (40 underheated, 70 undercooled). I
have already checked many of the parameters and all seems reasonable. Can I
do anything in order to reduce them? The only thing is to increase the
throttle range of the zone but I don't know if this is a solution.
Thank you for your help.
Regards,
Eva
Eva,
I found that if you can create a hourly report, you can determine which hours of which days cannot maintain set point. Then examine those hours to find out why they can't maintain set point. One issue I've found is pretty common is the that the space cannot heat up or cool down fast enough in the first few hours after the system turns on in the morning.
Hope this helps, Adam
Adam Rustige