I want to modeling OA system with electric resistance heating and fan coils without heating and without outside air (on chilled water). Look forward any suggestions...
Do you want the air supplied at a constant volume or variable volume? If CV
then use PSZ, if VAV then use VAVS or PVAV. To get rid of your heating coil
you can either un-select it or make it really, really small. Enter your
electric resistance heating as a supplemental or baseboard heat source.
That should be okay. Were you able to turn the heat off? If you can't, go to
the screen where you specify the capacity of the heating coil and input
something like .0000001.
Do you want the air supplied at a constant volume or variable volume? If CV
then use PSZ, if VAV then use VAVS or PVAV. To get rid of your heating coil
you can either un-select it or make it really, really small. Enter your
electric resistance heating as a supplemental or baseboard heat source.
Carol
2010/11/5 ????????? ??????
--
Carol Gardner PE
Yes, I have CV system. But PSZ working only with DX coil. And I use fan coils with chilled water coils.
Sincerely yours,
Mikhail Samoletov
That should be okay. Were you able to turn the heat off? If you can't, go to
the screen where you specify the capacity of the heating coil and input
something like .0000001.
Best,
Carol
2010/11/10 ????????? ??????
--
Carol Gardner PE