Trace-users Digest, Vol 22, Issue 3

1 post / 0 new

Jon,

I've entered pool loads in the past by creating a miscellaneous load in the internal and airflow loads library. Enter the peak load and sensible percent. Either select "None" or "Heating Load" as energy meter type. If you use heating load, a coil will become available in the System Assignments screen. You can assign the load from the pool to the pool boiler. I've used the activity factor of the pool during occupied and unoccupied periods to create a schedule to assign to the miscellaneous load which matches the occupancy schedule.

Due to the large latent load of a pool, you may see some strange things happening in TRACE. Make sure that you check the output reports to make sure that everything looks right.

Good luck,

Alex Chapin, E.I.T., LEED AP BD+C

Date: Mon, 10 May 2010 14:11:19 -0400
From: Jon Bruneau To: "trace-users at lists.onebuilding.org"

Subject: [Trace-users] Pool Dehumidification Equipment Sizing
Message-ID:

Content-Type: text/plain; charset="us-ascii"

Does anyone know of a good way to model indoor swimming pools in Trace? I estimated the pool evaporation rate using the formula from the ASHRAE Handbook - Applications but I'm unsure of the best way to plug this into the Trace model.

Thanks,
Jon