Thermostat Temperature Error

3 posts / 0 new
Last post

Hi all,

I'm really hoping one of you knows how to fix this problem please. In
some zones where I've set the thermostat so that it heats to 50F and
cools to 95F to prevent the cooling system from coming on, I'm getting
the following errors.

Any idea how to increase the temperature margins?

Your help is very much appreciated.

Many thanks,

Aswan

Aswan Ali's picture
Offline
Joined: 2011-09-30
Reputation: 0

The thermostat schedule has to be 50 and 95, not the min-supply-t. The
min-supply-t is usually around 50-55, or in 60's for underfloor.

-Rohini

Brahme, Rohini            UTRC's picture
Joined: 2011-09-30
Reputation: 0

It seems that you've changed the supply temperature. Double check that the min-supply temp is within the specified range, and then turn the cooling system off by using a schedule.