Thermal storage modeling issues: high cooling capacity and unmet hours

3 posts / 0 new
Last post

Dear eQuest users,

I need help in thermal storage modelling. The issue which I have faced is:

The project have 4 chiller (2200 TR each). To reduce peak load in day time,
I have modeled thermal storage of 8000 TR-h (95 MBTU) with charging and
discharging rate at 11.9 MBTU/h and 12 MBTU/h. To size each chiller
capacity, I modeled chillers as autosize in both case (with and without
thermal storage).

When there is no thermal storage the chiller sizing is 2386 TR each (4
chiller) with zero unmet hours and When I modeled thermal storage and a
chiller dedicated to thermal storage and other three are working as
supporting to thermal storage. The chiller size in this case are 3 chillers
of 3496 TR and one chiller of 1026 TR and 5467 unmet hours.

I am following procedure as mentioned in tutorial (attached). However, I
got unmet hours and higher cooling tonnage than without thermal storage
case.

Please help me to sort out this problem.

Regards,
Mayank Bhatnagar
Energy Analyst

Mayank Bhatnagar's picture
Joined: 2011-10-02
Reputation: 0

Mayank,
The using of thermal storage system in which an ice storage tank allows ice to accumulate during one period, and then thaws it for use during another. Since the unmet hours high try to increase your thermal storage capacity, also check in which space the unmet hrs are more and try to improve the supply cfm in zone air flow tab, also increase the size ratio in the system?

Soham Babu | Project Lead

[setty-logo]

| Fairfax, VA | Washington, DC | Baltimore, MD | New York, NY | Mysore, India
| M/E/P/FP Design Engineering | Project Management | Energy Management Services | Construction Management | Design-Build Services | Commissioning
| Voice 703.691.2115 Ext. 135 | Fax 703.691.8084 | Cell 984.411.2737 | soham.babu at setty.com | www.setty.com

This e-mail and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. If you are NOT the intended
recipient or the person responsible for delivering the e-mail to the intended recipient, be advised that you have received this e-mail in error and that any use, dissemination, forwarding,
printing or copying this e-mail is strictly prohibited.

Soham Babu's picture
Offline
Joined: 2011-09-30
Reputation: 0

Mayank,

Pls check your charging sch & discharging sch, this may help.

Kevin

???: Mayank Bhatnagar [mailto:mayank.23aug at gmail.com]
????: 2014?4?24? 13:29
???: equest-users at lists.onebuilding.org
??: [Equest-users] Thermal storage modeling issues: high cooling capacity and unmet hours

Dear eQuest users,

I need help in thermal storage modelling. The issue which I have faced is:

The project have 4 chiller (2200 TR each). To reduce peak load in day time, I have modeled thermal storage of 8000 TR-h (95 MBTU) with charging and discharging rate at 11.9 MBTU/h and 12 MBTU/h. To size each chiller capacity, I modeled chillers as autosize in both case (with and without thermal storage).

When there is no thermal storage the chiller sizing is 2386 TR each (4 chiller) with zero unmet hours and When I modeled thermal storage and a chiller dedicated to thermal storage and other three are working as supporting to thermal storage. The chiller size in this case are 3 chillers of 3496 TR and one chiller of 1026 TR and 5467 unmet hours.

I am following procedure as mentioned in tutorial (attached). However, I got unmet hours and higher cooling tonnage than without thermal storage case.

Please help me to sort out this problem.

Regards,
Mayank Bhatnagar
Energy Analyst

______________________________________________________________________
NOTICE: This communication and any attachments ("this message") may contain confidential information for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on this message is strictly prohibited. If you have received this message in error, or you are not an authorized recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies.

Tan, Kevin Zong-Neng's picture
Joined: 2014-03-15
Reputation: 0