System 4 - PSZHP Unmet Hours - "undefined" thermostat schedules

2 posts / 0 new
Last post

When you set the zone COOL/HEAT-TEMP-SCH to ?undefined?, there is no thermostat control in the zone and no unmet cooling/heating hours will be reported because the system is not trying to maintain the zone at any particular temperature. The cooling and/or heating thermostat schedules should be defined for at least the control zone of a single zone system.
~Bill

William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer

[cid:image003.jpg at 01D3A581.9CE47B20] [cid:image005.jpg at 01D3A581.9CE47B20]

134 South Fitzhugh Street Rochester, NY 14608

T: (585) 698-1956 F: (585) 325-6005

bbishop at pathfinder-ea.com www.pathfinder-ea.com

[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.

Bill Bishop's picture
Offline
Joined: 2012-02-25
Reputation: 7

Thanks Bill. Guess I need some more coffee :)

umesh atre2's picture
Offline
Joined: 2018-03-02
Reputation: 0