Spandrel Glass

12 posts / 0 new
Last post

I have a building with a very large amount of spandrel glass panels, which I modeled as glass since this seemed to be the only way to insert the panels into the exterior walls.
I would somehow like to re-assign the spandrel panels as another exterior component so they will be counted as part of the exterior walls in the LV-D report instead of glass.

Any idea on how this can be done?
Thank you,?Paul Diglio
87 Fairmont Avenue
New Haven, CT 06513

Paul Diglio's picture
Offline
Joined: 2011-09-30
Reputation: 400

Paul,
As I recall there IS a wall component called spandex glass in the Library. See if that solves your need.
John

Sent from Yahoo Mail on Android

On Wed, Dec 5, 2018 at 3:33 PM, Paul Diglio via Equest-users wrote: I have a building with a very large amount of spandrel glass panels, which I modeled as glass since this seemed to be the only way to insert the panels into the exterior walls.
I would somehow like to re-assign the spandrel panels as another exterior component so they will be counted as part of the exterior walls in the LV-D report instead of glass.

Any idea on how this can be done?
Thank you,?Paul Diglio
87 Fairmont Avenue
New Haven, CT 06513

_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send? a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

John Aulbach's picture
Offline
Joined: 2011-09-30
Reputation: 1

Paul ? to answer your question: painfully? It may not be that bad actually ? what?s your base wall type? For a curtain wall that is half spandrel and half vision glass, make the exterior opaque surface equivalent to the spandrel sections as a defined opaque wall construction, and then add the vision glass to that ? if you change the surface constructions in spreadsheet view it may not be that painful after all. The painful part will be deleting all of the current spandrel sections that are now defined as the base wall.

JRA ? I?m not sure of the purpose of the spandrel glass type in the library, I don?t know if that window object model has the capability to perform as if it were an opaque surface although this spandrel glass definition may be available to be selected?I?m not sure it would be an accurate choice. I wonder if it is a research entry that isn?t meant for the modeling public. Anyone used it?

David

David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Associate

Direct: (847) 316-9224 | Mobile: (773) 490-5038

Grumman/Butkus Associates | 820 Davis Street, Suite 300 | Evanston, IL 60201
Energy Efficiency Consultants and Sustainable Design Engineers

grummanbutkus.com | Blog | Facebook | Twitter

David Eldridge's picture
Offline
Joined: 2012-05-08
Reputation: 1

Hi Dave
I am not in front of my eQuest computer. But I think the spandrel has the u value of glazing without a shading coefficient, so would it not then be opaque. Makes no sense to me for glazing to be in a wall parametric library. I also think it is 1/4 inch, so I would add another spandrel wall and board insulation behind it.
We need another Engineering Manual written !!

Sent from Yahoo Mail on Android

On Wed, Dec 5, 2018 at 3:59 PM, David Eldridge wrote: #yiv0991509060 #yiv0991509060 -- _filtered #yiv0991509060 {font-family:Helvetica;panose-1:2 11 6 4 2 2 2 2 2 4;} _filtered #yiv0991509060 {panose-1:2 4 5 3 5 4 6 3 2 4;} _filtered #yiv0991509060 {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;} _filtered #yiv0991509060 {font-family:Roboto;}#yiv0991509060 #yiv0991509060 p.yiv0991509060MsoNormal, #yiv0991509060 li.yiv0991509060MsoNormal, #yiv0991509060 div.yiv0991509060MsoNormal {margin:0in;margin-bottom:.0001pt;font-size:12.0pt;font-family:New serif;}#yiv0991509060 a:link, #yiv0991509060 span.yiv0991509060MsoHyperlink {color:blue;text-decoration:underline;}#yiv0991509060 a:visited, #yiv0991509060 span.yiv0991509060MsoHyperlinkFollowed {color:purple;text-decoration:underline;}#yiv0991509060 span.yiv0991509060EmailStyle17 {font-family:sans-serif;color:#1F497D;}#yiv0991509060 .yiv0991509060MsoChpDefault {font-family:sans-serif;} _filtered #yiv0991509060 {margin:1.0in 1.0in 1.0in 1.0in;}#yiv0991509060 div.yiv0991509060WordSection1 {}#yiv0991509060
Paul ? to answer your question: painfully? It may not be that bad actually ? what?s your base wall type? For a curtain wall that is half spandrel and half vision glass, make the exterior opaque surface equivalent to the spandrel sections as a defined opaque wall construction, and then add the vision glass to that ? if you change the surface constructions in spreadsheet view it may not be that painful after all. The painful part will be deleting all of the current spandrel sections that are now defined as the base wall.

?

JRA ? I?m not sure of the purpose of the spandrel glass type in the library, I don?t know if that window object model has the capability to perform as if it were an opaque surface although this spandrel glass definition may be available to be selected?I?m not sure it would be an accurate choice. I wonder if it is a research entry that isn?t meant for the modeling public. Anyone used it?

?

David

?

?

David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP

Associate

?

Direct: (847) 316-9224 | Mobile: (773)490-5038

?

Grumman/Butkus Associates| 820 Davis Street, Suite 300 | Evanston, IL 60201

Energy Efficiency Consultants and Sustainable Design Engineers

?

grummanbutkus.com |Blog |Facebook |Twitter

?

John Aulbach's picture
Offline
Joined: 2011-09-30
Reputation: 1

John:
I am not sure how to get to the spandrel glass selection.? I do not see it in the library.? If I try to make another exterior construction, I have the option for a metal curtainwall but I do not see spandrels.

Anyway, these spandrel panels are uncoated glass on the exterior, air gap, painted glass on the interior with 6" of foam insulation between inner layer of glass and conditioned space.
David, I don't quite understand what you are suggesting, but the exterior walls will have a different u-factor than the spandrel panels, which is why I had to draw them separately.? I inserted the vision panels of the curtainwall on the exterior walls and inserted the spandrels separate from the vision panels of the curtainwall.? I was hoping there was some way I could edit the input file to change the spandrel panels to a new construction so they wouldn't show up on the LV-D report as glass.

Thanks for the responses,?Paul Diglio
87 Fairmont Avenue
New Haven, CT 06513

Paul Diglio's picture
Offline
Joined: 2011-09-30
Reputation: 400

Just checked. Spandrel Glass is the next to last listed material in the materials Library. How to look up its properties are for you young pups. If it is a material, I believe it will have only opaque properties.Again, it is shown as 1/4", so add another layer with an airspace between and whatever insulation is behind it.
Vulcans never lie..
On Wednesday, December 5, 2018, 4:38:51 PM GMT-8, Paul Diglio
wrote:

John:
I am not sure how to get to the spandrel glass selection.? I do not see it in the library.? If I try to make another exterior construction, I have the option for a metal curtainwall but I do not see spandrels.

Anyway, these spandrel panels are uncoated glass on the exterior, air gap, painted glass on the interior with 6" of foam insulation between inner layer of glass and conditioned space.
David, I don't quite understand what you are suggesting, but the exterior walls will have a different u-factor than the spandrel panels, which is why I had to draw them separately.? I inserted the vision panels of the curtainwall on the exterior walls and inserted the spandrels separate from the vision panels of the curtainwall.? I was hoping there was some way I could edit the input file to change the spandrel panels to a new construction so they wouldn't show up on the LV-D report as glass.

Thanks for the responses,?Paul Diglio
87 Fairmont Avenue
New Haven, CT 06513

John Aulbach's picture
Offline
Joined: 2011-09-30
Reputation: 1

I?ll toss some extra thoughts/experience into the pile:

My preferred approach to handling large amounts of spandrel glass is to start by taking advantage of the wizards? capacity to generate separate ?plenum? exterior wall sections (of height resulting from your ceiling inputs), to produce equivalent area to the spandrel glass on each orientation. Those separate sections are in part a by-product of the intent to distinguish the conditioned space/zone volume relative to the floor-to-floor height, but we can repurpose them!

I do not create glass on those ?plenums? wall sections, but rather just make a new ?spandrel? exterior wall construction in detailed mode and use custom user default expressions to automate assigning ?spandrel? vs. ?normal? constructions to each exterior surface as a function of their Z coordinate (0 = normal wall, else spandrel construction).

This can be combined with post-wizard manipulation of interior space/ceiling heights (which do not have to line up with the ?seams? separating plenum from normal walls), to capture cases where the spandrel actually extends below the ceiling line and ensure the conditioned volume is accurate around your perimeters. Be mindful that if the spandrel glass is largely incident on the conditioned volume it may be more appropriate to move them off the plenum spaces and onto the occupied spaces.

There is an aesthetic ?downside? to this approach to consider (according to some industry professionals I?ve worked with), but if someone *really* wants a pretty 3D model picture that looks like a fishbowl from the likes of eQuest (?), I?ll just add that you can generate some (apparently convincing) ?forgery? of extra windows by mis-using MSPAINT ? the duct tape of my graphical tool belt. And yes, I sleep at night just fine, thank you.

@David: I?m not sure about that library entry either, but I have in the past been convinced myself it was okay to use the simplified window glass definition option and

* specify a shading coefficient of zero (where SC is the ratio of solar energy transmitted relative to single pane float glass), and
* specify a U-value appropriate to the degree of insulation (though I?d leave this equivalent to the underlying glass layer(s) if it?s just painted panels ? run into that a couple times).
This modeling approach doesn?t pick up on all of the actual nuances of radiative* emissivity for painted-over windows, but it has for me been good enough for (literally) government work where there were much bigger problems to focus the energy model?s development around? If anyone has developed further best practices for handling ?high-e coatings? applied to mitigating unwanted transmissive solar gains, I am certainly all ears =).

~Nick

[cid:image001.png at 01D48D9E.25060E10]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric

D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com

15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States

[cid:image002.png at 01D48D9E.25060E10]

Nicholas.Caton at schneider-electric.com's picture
Joined: 2016-02-26
Reputation: 0

Great conversation!
I agree that spandrel panels should be modeled as EXTERIOR-WALL components and not WINDOWs.
My comments/hints that weren?t already mentioned below:

* The 1/4in Spandrel Glass material from the library should be entered as the first material in LAYERS (which are ordered outside to inside for exterior walls).
* The default library only has 1/4in Spandrel Glass but you can make any material layer as thick as you want by changing the THICKNESS.
* Absorptance: The percentage of solar radiation absorbed by the wall is input as ABSORPTANCE. This is a keyword for the CONSTRUCTION and is shown on the main tab/sheet of the wall construction. I assumed a glass spandrel panel would have a different absorptance than the default value of 0.700. After looking into it, I couldn?t find a good alternative value and it is probably all over the place depending on the glazing coatings/paints, air spaces and backing materials.
* Surface Roughness: The outside air film coefficient for exterior surfaces is a function of the surface roughness and wind speed. The ROUGHNESS keyword input is also on the main CONSTRUCTION tab/sheet. Glass and smooth painted surfaces have a ROUGHNESS of 6 per the DOE-2 help description. The default is 3.
* Emissivity: Infrared (heat) radiation to/from exterior walls is specified by OUTSIDE-EMISS which is a keyword of the EXTERIOR-WALL (not the CONSTRUCTION). The default value of 0.9 is close to the typical value for glass (0.84).
* I finally understand why they?re called curtain walls. They are not structural members. They are exterior coverings, as a curtain covers a window.
~Bill

William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer

[Pathfinder-EA-logo-2]T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com www.pathfinder-ea.com
134 South Fitzhugh Street
Rochester, NY 14608 [cid:image007.png at 01D48E11.062D7E60] Ask me why Carbon Fee & Dividend may be right for you.

Bill Bishop's picture
Offline
Joined: 2012-02-25
Reputation: 7

I second Nick?s approach to spandrel. I have not thought to use the plenum as a geometry generator. I?ll have to utilize that next time.

By code, spandrel is considered a wall construction that happens to have glass in it rather than a window you can?t see through. In my mind, that justifies using a wall construction and adjusting the exterior surface reflectance accordingly rather than try and model it as a window.

I hope everyone is having a great holiday season!

[ARCH | NEXUS]
DAVID W. GRIFFIN II
BEMP
ENERGY ANALYST
2505 E Parleys Way
Salt Lake City, UT 84109
Office 801.924.5028
archnexus.com
[Twitter][Facebook][Youtube][LinkedIn]

David Griffin II's picture
Joined: 2015-01-03
Reputation: 0

I'd like to thank every for their comments. I don't understand how the spandrels can be modeled as exterior walls since the exterior walls have a different u-factor and eQuest does not allow me to draw an exterior wall over an existing.? I think I understand Nick's approach, but it seems that the spandrels are not placed in the appropriate location and will influence the angle of solar gain?

To further complicate matters, this 5 story building does not have a plenum ceiling, the floor deck above is visible in the space below.?

I was able to successfully model the spandrels by using a different type of glass, then entering the U-factor by the simplified method and zeroing the Sc and reflectance.? The problem is that LV-D? reports the spandrels as part of the glass, so it throws the window to wall ration calculations off.
I found the simplest method was simply remove the spandrels (+100) and run the LV-D report to get the actual area of the vision glass.

Regards,?Paul Diglio
87 Fairmont Avenue
New Haven, CT 06513

203-415-0082

Paul Diglio's picture
Offline
Joined: 2011-09-30
Reputation: 400

Some of the mixup might be that some walls are for sake of argument in round figures 50% spandex and 50% vision glass, and some minor percent structure and other.

Other buildings might 33% structure/masonry/etc and 33% spandrel, and 33% vision glazing.

So a common approach in case a is spandrel = wall, windows are windows.

For case B you need two different walls, plus windows in one or both, and how you model the two walls may be important to your zone loads, but look odd in the rendering even if it is thermally equivalent and geometrically expedient.

If you have a photo of the facade you are talking about it might help to sync all of us.

DSE Mobile

David Eldridge's picture
Offline
Joined: 2012-05-08
Reputation: 1

HI David:
?Please find attached a rendering of the building I am modeling.? Note there are two types? of exterior walls, the brick covered columns and sills and the rest is ACM.? You can see the spandrel panels under and above some of the windows in a sort of grey-blue color.? The spandrels total about 7,000 square feet and the windows about 30,000 square feet.? There is some screening on the ends of the building which may or may not be eliminated.

I was able to model the two exterior wall types and added the spandrels as a different glass type.? Yes, the spandrel consists of an exterior clear lite, air gap, painted interior lite and 6" of blown-in foam between that and the conditioned space.? It actually has a better U-factor than the ACM walls.
Thank you,
?Paul Diglio