All,

On the baseline model for a project, I continue to get the following
error despite several attempts to remedy: SPACE E13 NNW Perim Spc
(M.NNW51) has no ZONE - one is required.

My attempts to fix it have included:

* trying to locate a ZONE definition within the program -
unsuccessful
* directly editing the BDL file by pasting a missing section from
the Proposed BDL file - didn't work; errored out anyway (see below)
* deleting the error at the end of the BDL file - didn't work;
errored out anyway

I've included the text below from the Designed (proposed) BDL file. I
believe the bolded text is what is missing from the Baseline BDL file.

The text below is from the Baseline BDL file indicating where I think
the missing text would go.

*90096* SPACE = "E13 North Perim Spc (M.N50)"

*91135* "E13 Sys2 (PMZS) (M.N50)" = SYSTEM

*90097* ..

*91136* TYPE = PTAC

*90098* "E13 Sys2 (FC) (M.NNW51)" = SYSTEM

*91137* HEAT-SOURCE = HOT-WATER

*90099* TYPE = FC

*91138* BASEBOARD-SOURCE = NONE

*90100* HEAT-SOURCE = HOT-WATER

*91139* SIZING-RATIO = 1

*90101* BASEBOARD-SOURCE = NONE

*91140* HEAT-SIZING-RATI = 1.25

*90102* SIZING-RATIO = 1.15

*91141* COOL-SIZING-RATI = 1.15

*90103* MAX-SUPPLY-T = 95

*91142* MAX-SUPPLY-T = 90

*90104* MIN-SUPPLY-T = 55

*91143* MIN-SUPPLY-T = 55

*90105* ECONO-LIMIT-T = 65

*91144* FAN-SCHEDULE = "S2 Sys2 (PMZS) Fan Sch"

*90106* OA-CONTROL = FIXED

*91145* FAN-CONTROL = FAN-EIR-FPLR

*90107* FAN-SCHEDULE = "S2 Sys2 (FC) Fan Sch"

*91146* SUPPLY-STATIC = 0.15

*90108* SUPPLY-STATIC = 0.5

*91147* SUPPLY-EFF = 0.507515

*90109* SUPPLY-EFF = 0.328

*91148* HW-VALVE-TYPE = TWO-WAY

*90110* HW-VALVE-TYPE = TWO-WAY

*91149* HW-COIL-DT = 50

*90111* HW-LOOP = "Hot Water Loop"

*91150* HW-LOOP = "Hot Water Loop"

*90112* CHW-VALVE-TYPE = TWO-WAY

*91151* COOLING-EIR = 0.3667

*90113* CHW-LOOP = "Chilled Water Loop"

*91152* FURNACE-HIR = 1.24067

*90114* FURNACE-HIR = 1.24067

*91153* ..

*90115* ..

*90116* "E13 NNW Perim Zn (M.NNW51)" = ZONE

*91154* "E13 North Perim Zn (M.N50)" = ZONE

*90117* TYPE = CONDITIONED

*91155* TYPE = CONDITIONED

*90118* MIN-FLOW-RATIO = 1

*91156* MIN-FLOW-RATIO = 1

*90119* FLOW/AREA = 0.5

*91157* FLOW/AREA = 0.5

*90120* OA-FLOW/PER = 1.0846

*91158* OA-FLOW/PER = 1.0846

*90121* DESIGN-HEAT-T = 72

*91159* DESIGN-HEAT-T = 72

*90122* HEAT-TEMP-SCH = "S2 Sys2 (FC) Heat Sch"

*91160* HEAT-TEMP-SCH = "S2 Sys2 (PMZS) Heat Sch"

*90123* DESIGN-COOL-T = 75

*91161* DESIGN-COOL-T = 75

*90124* COOL-TEMP-SCH = "S2 Sys2 (FC) Cool Sch"

*91162* COOL-TEMP-SCH = "S2 Sys2 (PMZS) Cool Sch"

*90125* SIZING-OPTION = ADJUST-LOADS

*91163* SIZING-OPTION = ADJUST-LOADS

*90126* SPACE = "E13 NNW Perim Spc (M.NNW51)"

*91164* SPACE = "E13 North Perim Spc (M.N50)"

*90127* ..

*90128* "E13 Sys2 (FC) (M.C52)" = SYSTEM

Please let me know of any thoughts or suggestions you may have. Any
help is appreciated.

Regards,

James D. Waechter, P.E., LEED A.P.

James D. Waechter's picture
Joined: 2011-09-30
Reputation: 200

James,

You'll need to edit the .inp file instead of the .bdl file. The .bdl file
is generated from the .inp & .pd2 files, and changes made to it will be
discarded every time you save the project.

You'll need to create a new zone and reference the space in question either
from the .inp file or the equest interface.