Hi eQUESTers,

I calculated the annual BTUs required for a HW snow melt loop. What?s the easiest way to input this into eQUEST?

via Equest-users's picture
Joined: 2016-07-15
Reputation: 400

The Sequence of Operations should include the control sequence for the snow melt system. A typical sequence might stipulate, ?When OAT is below 35?F and on detection of snow or rain, start the snow melt pump?. I use the hourly weather data in a spreadsheet to determine the number of hours the system is running. Note, the CWEC weather files include the snow/rain flag. I am not sure if the EPW files include this flag.