Slab extending through wall

15 posts / 0 new
Last post

I am evaluating a new 10-story hotel design that is proposing glass curtain walls and pre-tensioned concrete floors that project beyond the walls. On 3 sides the projections are minimal (6 inches). However, on one side, the projections extend about 3 ft.

For the small projections, I intent to use the following method recommended in the thread below. "In screen 4 of 25 of the DD shell wizard you can specify "Slab Penetrates Wall Plane" (check box)."

I am interested in any tips for modeling the thermal impacts of the larger projections. Thoughts? (I plan to use window shading for the light/shading impacts.)

I am hopeful that the analysis will help convince the design team to incorporate some insulation and thermal breaks!

Thanks in advance!
Kevin
Mon Dec 6 11:45:18 PST 2010
Previous message: [Equest-users] balcony
Next message: [Equest-users] Shading
Messages sorted by: [ date ] [ thread ] [ subject ] [ author ]

In screen 4 of 25 of the DD shell wizard you can specify "Slab
Penetrates Wall Plane" (check box). If you do, eQUEST created a new
wall type of height equal to your slab thickness and composed of 1' of
concrete plus any slab edge insulation you specify on the same wiz
screen. That provides a parallel path for the heat transfer from the
balcony or slab edge. Not exactly 2D heat transfer modelling -- but at
least you aren't ignoring the effect of the slab edge or balcony.

Kevin Coleman, CEM, LEED AP 

Coleman, Kevin's picture
Offline
Joined: 2013-11-05
Reputation: 0

Hello Kevin,

I would recommend looking at this report prepared for ASHRAE TC4.4 by Morrison Hershfield.? They have some pretty good data which may help you out.

http://www.morrisonhershfield.com/ashrae1365research/Documents/MH_1365RP_Final_%20small.pdf

Byron D. Burns, EIT, BEMP

Byron Burns's picture
Offline
Joined: 2012-07-18
Reputation: 0

Kevin,

I'm fairly sure eQUEST is not even going to closely approximate the heat loss/gain accurately unless you dial the loads in manually which means you have to calculate them by hand first. I suggest referring to ASHRAE-D-RP-1365 for guidance on estimating the loads. The section you are interested in starts on page 35.

Thanks,

David W. Griffin II

David Griffin's picture
Offline
Joined: 2011-12-07
Reputation: 0

Here's a timely report on effective R-values of assemblies with slab/balcony thermal bridges:
The Importance of Slab Edge and Balcony Thermal Bridges

Regards,
Bill

William Bishop, PE, BEMP, BEAP, LEED AP

Bill Bishop's picture
Offline
Joined: 2012-02-25
Reputation: 7

Great report ..... thanks.

Michael Hupel, B.Tech, CEM, LEEDRAP

Michael Hupel's picture
Offline
Joined: 2012-01-20
Reputation: 0

Some more references

1. See attached " A Bridge too far' from the ASHRAE Journal, Oct 2007.
(This is freely available on the internet)

2. Also read the ASHRAE Journal July 2012 issue Thermal Bridge
Redux.
*Joseph W. Lstiburek.* P. 60. July. (Will require ASHRAE login info)

3. There was a presentation in the 2012 ASHRAE Energy Modeling Conference
Atlanta that detailed out the impact of extended slabs and the effective
R-values. Although I do not have details of that presentation, maybe
someone does.

Regards

Ramya Shivkumar

r s's picture
r s
Offline
Joined: 2013-07-02
Reputation: 2

To me the most interesting part of the report isn't the conclusion that thermally broken balconies and slab edges give significantly better thermal performance (we all know that intuitively). Instead it gives a way of back checking what I would consider to be "standard practice" for calculating area-weighted U-factor for these same assemblies using default ASHRAE U-values to sophisticated thermal model results. Here are my thoughts, checking my calcs and comments appreciated.

Executive summary: It looks like our standard assembly performance tables and area-weighted U-factor calculations get us "close enough" to the results from this report that it doesn't seem to suggest we should switch methodologies.

Comparison calculation for steel-framed walls (stud insulation + exterior rigid):
For a 16" OC metal stud wall, R-12 Batt cavity insulation and R-5 continuous rigid insulation, the report states that the Effective R-value for the wall + slab will be R-7.4. This is based on 8'8" floor-to-floor, and 8" slab.

Using ASHRAE 90.1-2007 Table A3.3 for steel framed walls, we would get an effective U-factor for the wall portion of U = 0.0785 (interpolating between the R-13 + R-11 batt values). If we use Table A3.1A for the exposed slab edge (assuming 8" normal weight solid concrete walls), we get a U-factor of U = 0.740 for the slab edge.

Doing an area weighted U-factor calc: Ueff = U1*A1+U2*A2/(A1+A2) or in this case, factoring out the Length of the wall section we use: U1*H1+U2*H2/(H1+H2) = (0.0785*8 + 0.740*8/12)/(8+8/12) = 0.1294 or an effective R-value of 7.73, which is pretty close to the R-7.4 claimed, a difference of about 4% in U-value. Maybe I'm cynical, but to me that seems close enough.

I only spot checked this assembly, so maybe there is more impact with different construction types.

Another interesting tid-bit: Apparently the much vaunted fin-effect is actually pretty minimal. If you look at the results of the exposed slab-edge condition vs the full balcony fin-effect, the balcony scenario actually shows slightly BETTER thermal performance. Odd.
[cid:image003.png at 01CED972.79A92370]
[cid:image004.png at 01CED972.79A92370]

Nathan Miller - PE, LEED(r)AP BD+C, CEM

Nathan Miller's picture
Offline
Joined: 2011-09-30
Reputation: 200

Nathan,
In the Balcony calculation, are you accounting for both the 'edges' and 'exposed area' of the balcony ?
In my opinion, a concrete balcony should be accounted for as a heat exchanger with 3 surfaces (perimeter edges, upper surface, lower surface); it looks like you are only accounting for the edges.

I had a 'heated' discussion about this with a vendor recently and the above is more or less a conclusion of that. Some of the structural thermal break products can be too expensive to justify based on energy savings, if area of balconies is not accounted for; the bigger your balcony, the better your payback from thermal breaks.

Best,

Kapil Upadhyaya, LEED AP

Kapil Upadhyaya's picture
Offline
Joined: 2012-07-03
Reputation: 0

Kapil,

No, I am only accounting for the ?face? of the balcony, as if you sheared it off at the plane of the wall.

That is my point, the fancy thermal modeling in the report, which is supposed to account multi-dimensional fin-effects doesn?t come out with much different result than if you just take a simplified approach like a typical UA-trade-off calculation (one directional heat transfer, no fin effects accounted for). So by that line of reasoning, you would likely be OVER ESTIMATING heat loss if you throw in all three heat-exchanger surfaces that you mention in your methodology. I?d be interested if you compared your calculation results to the thermal modeling in the report if you feel like a little intellectual exercise.

Nathan Miller - PE, LEED?AP BD+C, CEM

Nathan Miller's picture
Offline
Joined: 2011-09-30
Reputation: 200

It surprises me that the report indicates a better R-value for the fin
effect of a concrete balcony vs. the simplified exposed slab edge approach.
Seems to violate the basic teachings heat transfer 101. I can't think of
a logical explanation of how that could be the case and would chalk it up
to intricacies of the modeling tool. However I agree with Nathan that
since the report doesn't show nearly any difference between the fin effect
vs. the exposed slab edge that it's not necessarily worth the complication
in modeling unless the balcony slabs are the focus of the study.

Robby Oylear's picture
Offline
Joined: 2011-09-30
Reputation: 202

My guess is that the 3-D thermal model uses a pretty simple surface
convection/radiation assumption, like an air film. To properly model
the fin effects, the thermal model would need to be coupled with CFD and
a radiation model to account for the more complex heat transfer effects
associated with "fins".

David Reddy4's picture
Offline
Joined: 2012-03-30
Reputation: 0

I would think the effect of the balconies would increase the thickness
of the exterior laminar layer on the building. The air flow is
perpendicular to the fins. In calm conditions the main driver is going
to be stack effect. The exposed edges are on a flat surface and would
have a normal boundary layer. Without a projection they would offer
little resistance to the airflow from the stack effect.
A 60% reduction in effective R-value for a building is quite a
significant effect depending on where you are starting from. A high
ratio glass building is a low starting point.
Bruce Easterbrook P.Eng.
Abode Engineering

Bruce Easterbrook's picture
Joined: 2011-09-30
Reputation: 0

I think the key factor in comparing the case of a balcony and a slab edge flush with the exterior wall face is the effect of the balcony on the temperature of the concrete at the plane of the exterior wall.

For the slab edge: the temperature of the slab edge depends on how quickly heat is transferred to the outdoor air, with a thin boundary layer of air slowing the transfer of heat between the concrete and the outdoor air. The temperature of the concrete will depend strongly on the rate heat transfer from the concrete to the outdoor air over a small surface area.

For the balcony: the temperature of the concrete in the plane along the exterior wall surface will depend on the rate of heat transfer to the protruding balcony. The temperature of the balcony will depend on how quickly heat is transferred to the outdoor air over a much larger surface area than in the slab edge case. Since the heat transfer to the outdoor air from the balcony happens over a much larger surface area, it is possible for the temperature of the balcony to be closer to the temperature of the outdoor air than in the slab edge case in which case the balcony would lose heat faster.

In determining which configuration leads to higher rates of heat loss, a lot depends on how the transfer between the concrete surface and the outdoor air is modelled. This strikes me as the item of greatest uncertainty in the Morrison Hershfield report, and the report does call this out on page 23: ?Selecting heat transfer coefficients for accurate calculations can be a challenge for components where a larger percentage of the overall thermal resistance is the surface resistance. However, the thermal performance of insulated opaque building envelope components is the primary output of this project."

All the best,
Dan

?
Daniel Knapp, PhD, P Phys, LEED? AP O+M

Daniel Knapp's picture
Offline
Joined: 2011-09-30
Reputation: 0

I wasn?t saying the effect of exposed slab edges and balconies is insignificant. What I was saying is that I don?t see much difference in using the thermal performance for those assemblies modeled in the report vs. using typical practice of just calling balconies and exposed slab edges ?uninsulated concrete walls? and assigning that default U-factor to them (hence you would have about a 1? high uninsulated concrete wall and an 8-9? high typical opaque wall).

Nathan Miller - PE, LEED?AP BD+C, CEM

Nathan Miller's picture
Offline
Joined: 2011-09-30
Reputation: 200

True. I was thinking more on the comparison of insulation efficiency.
These buildings as modelled and designed have R-18.5 of insulation and
the net effect to the envelope is R-10 or less. Comparing this type of a
building and our current housing code in Canada where glass is limited
to 17% of the wall area, R-4+ glass, wall insulation of R-28 and roof
insulation of R-60 and intense scrutiny of thermal breaks, well lets
just say they are energy pigs. When you have an R-2 or 3 glass wall a
little bit of R-2 concrete in there doesn't make much difference. Even
if you stick a fin out 8' is still doesn't make much difference.
The research is interesting and quantifies the effect. It also shows
current modelling does a reasonable job of reflecting what is going on.
But for the building as a whole and the model it can have a small impact
if it isn't efficiently designed. The impact of how it is modelled has
an even smaller impact. 60% of R-20 is significant, 60% of R-2 is
meaningless and a 3% error in that is nothing.
The big picture is getting lost in all this work. We are using a
modelling technique in which a 10% error is considered very accurate, a
good model. Many of the early LEED buildings, as built, deviated from
the models by 100% brand new. Many others that did ok on day one were
way out by year 5. The models weren't the main problem, it was
application. Modelling is expensive. It seems to me that sometimes too
much time, effort and money is spent chasing less than a percentage
point of gain. There is a science to keeping the model efficient as
well. Also, the main way a model is used is as a "what if" test
platform. Holding most things constant and trying variations. This
reduces error as well. But if the sealing contractor does a poor job
and the building takes a 15% hit a little bit of R-2 concrete on the
envelope doesn't matter very much.
The science is great, this type of research is very illuminating and
will drive better design. The application of our technology, the tools
we use and how we use them is the biggest variable affecting the
efficiencies we are trying to achieve.
Bruce Easterbrook P.Eng.