Simulation output report file

3 posts / 0 new
Last post

Folks,

In one of my project, I have specified capacity of heating system in
proposed model, but same doesn?t reflect in the simulation output
report file. Any idea??

Thanks
GK

GK Pandian's picture
Offline
Joined: 2011-09-30
Reputation: 0

I would check that all applicable sizing ratios are set to 1. The specified
heating capacity of an air-side system will be adjusted by Heating Sizing
Ratio entered on Heating -> Coil Cap / Control tab, and Sizing Ratio
entered on Basics tab of the Air-Side HVAC System Parameters window.

Good luck,

Maria

Maria Karpman's picture
Offline
Joined: 2011-09-30
Reputation: 0

I would also check the elevation your project is at in eQuest. I had a
project in CO that was at 5,900 ft and eQuest used a altitude-adjustment
factor on all my inputs of 1.24 to account for this and it tripped me up
for a while. I think this was being applied to capacities and airflow rates
I specified.

-Neil