Simulation Error Message

2 posts / 0 new
Last post

Hello All,

Every time that I try to run a simulation of my building using e-quest an error message pops up that says "errors during hvac simulation or design calculations. See sim file for details." I went under the simulation file and found the error and it was for one of my air handling units, and it said that "cooling coil leaving temperature must be at least 6?F higher than entering water temp." I've been looking all over in the different files and pretty much my question is where do I go in order to change this to be correct? Another question is every time that I go to make a custom roof in the detailed edit wizard and go back to the building creation wizard the custom roof changes back to the previous shape and I was wondering why that was.

Thanks.

Christopher Sturdivant

Christopher Sturdivant's picture
Joined: 2011-09-30
Reputation: 0

Hi Christofer,
About the cooling coil error, try reducing mass flow in this water circuit.
About loosing information you change in the detailed interface once you
go back to the wizards, eQuest is just like this. Make sure you have
done everyting you need within the Wizard before you go to introduce
changes in the detailed interface!

*Xavier Garc?a Casals*

=?ISO-8859-1?Q?Xavier_Garc=EDa_Casals?='s picture
Joined: 2011-09-30
Reputation: 0