All;
Have a project using a run-around loop to recovery sensible energy from laboratory exhaust fans. I have reviewed the archives and my own memory, but this is leaving me scratching my head. I also recall a recent (maybe?) discussion on Zone vs System exhaust that may directly feed into this - but cannot find it.

If the lab hood exhaust is put in at the zone level, eQuest won't do energy recovery on this air-stream, as zone exhaust goes 'outside', yes?

My current thought is to configure the VAV AHU to have either 'Sensible HX' or 'Heat Pipe' and also have self-contained ERV fans. I'd input the Exhaust fans in as scheduled and then put a low/0 power fan for supply since there really isn't such. The OA is moved by the primary supply fan. I'd also calculate a 'HX power' or the run-around pump. I'd have 0 zone exhaust; exhaust only at the System level.

Can anyone comment on this approach or advise on how to best approach?

Thanks,
DARIC R ADAIR PE, CEM, BEMP
Mechanical Engineer, Energy Analyst

Henderson Engineers
8345 Lenexa Drive, Suite 300 | Lenexa, KS 66214
Tel (913) 742-5530
daric.adair at hendersonengineers.com

hendersonengineers.com

Licensed in KS

Sending me large files? Please use Henderson File Share | TX ID #F-001236

________________________________

This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited. If you received this email in error, please immediately notify administrator at hendersonengineers.com.

Daric Adair's picture
Offline
Joined: 2017-10-21
Reputation: 0

I believe zonal exhaust can be captured in the relief airstream for ERV, but getting the relief airstream correct means getting a solid enough handle on everything else: return/supply/infiltration/exfiltration.

Following is the last diagram on this matter that I drew up for myself.

I'm open to comment/corrections, but this answers at least some of your questions, I believe:
[(AV3 ON) *Wi? 'Vr*ez -3d1*5m0 JM0d J9h?y3]

[cid:image002.png at 01D36A02.0DFC6540]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric

D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com

15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States

[cid:image003.png at 01D36A02.0DFC6540]

Nicholas.Caton at schneider-electric.com's picture
Joined: 2016-02-26
Reputation: 0