Hello,
I?m modeling a VAV system and the building is using more energy for
zone-level reheat in the summer months than I would expect. Any thoughts
on what this could be from?
*Mike Campbell, E.I.T., LEED AP O+M*
*Sustainability Specialist*
*Sustainable Solutions Corporation*
Office: 610-569-1047
Mobile: 609-923-1743
www.SustainableSolutionsCorporation.com
*Sustainable Solutions Corporation is WBENC and BCorp Certified.*
*This email message and any attachments are for the sole use of the
intended recipient(s) and may contain confidential and privileged
information. Any unauthorized review, use, disclosure or distribution is
prohibited. If you are not the intended recipient, please contact the
sender by reply email and destroy all copies of the original message and
any attachments.*
What kind of building, and what is your expectation?
The zone minimum airflow may be higher than the actual (or design?) minimums, resulting in excess reheat. This is probably the most common explanation.
If the building has higher minimum airflows by design (such as healthcare or laboratory spaces) then the reheat energy calculated by the program may be accurate.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
Okay, that is probably the issue. I am modeling a lab with 100% outside
air. The zones appear to be supplying the minimum supply air nearly all
the time, which I assume would result in over-cooling without the reheat.
Thank you
*Mike Campbell, E.I.T., LEED AP O+M*
*Sustainability Specialist*
*Sustainable Solutions Corporation*
Office: 610-569-1047
Mobile: 609-923-1743
www.SustainableSolutionsCorporation.com
*Sustainable Solutions Corporation is WBENC and BCorp Certified.*
*This email message and any attachments are for the sole use of the
intended recipient(s) and may contain confidential and privileged
information. Any unauthorized review, use, disclosure or distribution is
prohibited. If you are not the intended recipient, please contact the
sender by reply email and destroy all copies of the original message and
any attachments.*
*From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
Behalf Of *David Eldridge
*Sent:* Wednesday, July 16, 2014 2:31 PM
*To:* equest-users at lists.onebuilding.org
*Subject:* Re: [Equest-users] Reheat energy in summer
What kind of building, and what is your expectation?
The zone minimum airflow may be higher than the actual (or design?)
minimums, resulting in excess reheat. This is probably the most common
explanation.
If the building has higher minimum airflows by design (such as healthcare
or laboratory spaces) then the reheat energy calculated by the program may
be accurate.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
*Grumman/Butkus Associates*
*From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org
] *On Behalf Of *Michael
Campbell
*Sent:* Wednesday, July 16, 2014 1:24 PM
*To:* equest-users at lists.onebuilding.org
*Subject:* [Equest-users] Reheat energy in summer
Hello,
I?m modeling a VAV system and the building is using more energy for
zone-level reheat in the summer months than I would expect. Any thoughts
on what this could be from?
*Mike Campbell, E.I.T., LEED AP O+M*
*Sustainability Specialist*
*Sustainable Solutions Corporation*
Office: 610-569-1047
Mobile: 609-923-1743
www.SustainableSolutionsCorporation.com
*Sustainable Solutions Corporation is WBENC and BCorp Certified.*
*This email message and any attachments are for the sole use of the
intended recipient(s) and may contain confidential and privileged
information. Any unauthorized review, use, disclosure or distribution is
prohibited. If you are not the intended recipient, please contact the
sender by reply email and destroy all copies of the original message and
any attachments.*