John,
The second DHW heater had an entered capacity of "0.000". I entered a
non-zero capacity and the DHW energy use jumped. (I assume you are
looking for energy consumption and not just what the loop loads are on
the PS-D report.)
As an aside, remember when entering capacities for boilers and DHW
heaters in eQUEST that the units "MBtu/h" are millions, not thousands of
BTU. (Or do you really have a DHW heater that needs 17,000 gpm? :-))
Regards,
William Bishop, EIT, LEED(r) AP