Modelling simplification for structural concrete columns

14 posts / 0 new
Last post

Hi everyone,

I'm wondering how best to simplify a model when considering structural
concrete columns.
My modelling is in the context of the LEED whole building energy modelling.
So I'm concerned with accuracy as much as acceptability by the LEED
reviewers. I've read the ASHRAE 90.1 user's manual but didn't find a
satisfactory answer.

Here's an example:

----
wall | | wall
-------| |------
| |
----
concrete column

I can see 3 options for simplifying, each with its own issues:

1. Make the external surface of the column at the same level of the
surrounding walls and model the column surface as having its true thickness
. The issue is that it alters the area of the space inside and doesn't
account for the shading effect of the column.

2. Follow the internal boundary of the column, which introduces 3 surfaces.
Not sure what construction thickness to assign to these surfaces. This
preserves the internal space area but alters the shading effect of the
column.

3. Follow the external boundary of the column. This also introduces 3
surfaces. Not sure what construction thickness to assign to these surfaces
either. It preserves the shading effect of the column but alters the area
of the internal space.

I'm leaning towards option 1. What do you think? Are they other better
options I overlooked?

Of course, things get a bit more complicated when the walls either side are
not aligned or in the same plan...

Thanks!
Patrick

Patrick Bivona's picture
Offline
Joined: 2012-11-12
Reputation: 0

Group,
Please do correct me if I am wrong--->>

- ASHRAE 90.1 does not require thermal bridging to be modeled in the
baseline.
- ASHRAE 90.1 does not require internal mass to be modeled in the
baseline.
- ASHRAE 90.1 does not require self shading to be modeled in the
baseline.
- ASHRAE 90.1 requires a light weight wall assembly for the baseline.

So the conclusion is that this does not need to be modeled in the baseline
and the question becomes how to model this in the proposed building, or
actually "what gets the project more LEED credits" If I where to do it I
would: (in E+)

- Ignore the shading element of the concrete pillars and consider the
walls that separate the zones the only thing that matters for shading.
- Dependant on the other wall construction-- if mass than add the
thickness to the total wall area-- if steal framed, wood&other or metal
than bridge wall with column and add internal mass to account for thermal
mass.

My conclusion is your #1 should be fine, especially if your not attempting
to get credit for the exposed thermal mass..

Jeremiah Crossett2's picture
Joined: 2012-12-14
Reputation: 0

To the original post, I would use the line of the wall and ignore the columns. If you feel that there is a considerable shading effect, then use side fins or a building shade. Look at a section of wall the width of one column spacing as calculated the combined U value and thermal mass of the wall to see if the columns will have enough of an effect to make it worth modeling. I don't know how large the columns you are referring to are but it is likely that they would have a negligible effect on the model as a whole, especially when you consider the uncertainty of other values that are input. There is a line in Table G3.1.5 saying that other envelope assemblies that cover less than 5% of the total area need not be explicitly model and can be averaged into other wall assemblies.

As to Jeremiah's post,

* ASHRAE 90.1 does not require thermal bridging to be modeled in the baseline.
Thermal bridging should also be taken into account when calculating wall and floor U Values. External un-insulated assemblies must be explicitly modeled.

* ASHRAE 90.1 does not require internal mass to be modeled in the baseline.
I don't think any internal constructions are addressed in 90.1. Generally the effect of any internal walls will be negligible compared to the external walls unless your typical wall is heavy weight like a concrete block wall. Some schools are like this. Either way I would say internal mass would not need to be included in the baseline since the baseline is a metal framed building, which implies GWB internal walls.

* ASHRAE 90.1 does not require self shading to be modeled in the baseline.
* ASHRAE 90.1 requires a light weight wall assembly for the baseline.
The baseline should used a metal framed wall, which still has some mass effects that are required to be modeled. The way I understand it, a "light weight" wall refers to neglecting the mass effects of walls in your calculations.

Brendan Hall

Hall, Brendan's picture
Offline
Joined: 2011-09-30
Reputation: 1

Hi Patrick,

Another choice is to use a tool like Therm to calculate the u-value of a typical section of your wall assembly and then create a uniform wall with that average u-value. This is an acceptable strategy for a whole building energy model for LEED. You can make it more complicated but it probably won't change the outcome unless you're also carefully calibrating the interior surface massing, furniture massing, interior surface reflectance and emittance values and using custom glazing performance data.

Most modeling software also has the ability to enter a window setback that will allow you to account for the shading of the column projections, or you can just add fins to the windows to pick up this shading effect.

Mike

Sent from my iPad

Michael Tillou's picture
Offline
Joined: 2011-10-02
Reputation: 0

Brendan,

I expanded on some of the points you made below.

Mike

Sent from my iPad

Michael Tillou's picture
Offline
Joined: 2011-10-02
Reputation: 0

Thank you all for your feedback!

Patrick Bivona's picture
Offline
Joined: 2012-11-12
Reputation: 0

FYI.

ASHRAE RP1468, just finished, which provides BIM-to-thermal modeling examples, contains example modeling DOE2 input files and BIM files for concrete thermal bridging, and other examples like curved windows, etc.

The final report can be I obtained from Mike Vaughn at ASHRAE.

Jeff S. Haberl, Ph.D., P.E., FASHRAE, FIBPSA

Jeff Haberl2's picture
Offline
Joined: 2011-10-02
Reputation: 200

Patrick,

I wouldn't worry about the construction thickness, this has little bearing on the overall energy consumption. Any energy model is an estimation of the actual geometry and if it's out by 1% on floor area it's not going to be significant overall. Ensure any shading effects on windows are picked up (Some software allows you to do this with a shading device object, others might need it specified in the window setup) and that the overall area weighted U-value for your wall, including the concrete column areas is correct. Ensure your baseline is modelled in a consistent way and the LEED reviewers won't have anything to question. It's when you try to gain unfair advantage that they will have an issue.

Hope that helps.

Edwin Wealend

Wealend, Edwin's picture
Offline
Joined: 2013-02-18
Reputation: 0

Patrick,

I frankly think that you're looking at the modeling of building geometry
in simulation programs too literally. Please keep in mind that in the
end all
the simulation programs are just doing hundreds of one-dimensional heat
flow calculations through thousands of time steps. Wall thickness is needed
only to compute the heat flow characteristics (U-value, response factor,
transfer function, etc.) but is not modeled explicitly in the
simulation, i.e.,
walls have no thickness in the simulations. Similarly, the space volume
is used only to determine the amount of air participating in the space
heat balance, so therefore you should always input the actual enclosed
volume, even if it does jive with the dimensions of the enclosing
surfaces. If you're concerned about the shading effect of the columns,
they can be model them as narrow vertical building shades with widths
equal to the protruding part of the columns, but if the walls are
opaque, the effect must be extremely small.

However, I think you're ignoring what I think is the most significant
heat transfer aspect of these columns, which is the two-dimensional
conduction through them, because the columns act like stubby fins on the
wall, particularly if they're solid concrete with no insulation. That's
where I would concentrate my energies if I wanted to get the modeling right.

To do that, you would really have to model the wall-column-wall assembly
with a 2-D conduction program like THERM (available from LBNL), although
that was written for modeling window frames and can only output a
steady-state U-value. I still have a 2-D conduction program written in
Fortran called WALFERFN (sounds German, doesn't it ? but the acronym
stands for WAll Finite Element Response Factor New :-) ) that I use to
calculate response factors for composite walls, but that can only handle
planar surfaces.

Joe Huang

Joe Huang's picture
Offline
Joined: 2011-09-30
Reputation: 406

Sorry, caught a couple of typos, meant to write in the second paragraph,
"...even if it doesn't jive.." and "they can be modeled..."

Joe

Joe Huang's picture
Offline
Joined: 2011-09-30
Reputation: 406

Joe, Edwin,

I take your point that I'm probably too literal in my attempt at modelling
the geometry of this wall.

Thanks for the collegial suggestion about THERM. It seems really good and
I'm pretty sure it's going to be useful to me further down the line.

The building I'm modelling is a tower with a square floor section of
1400m2. There are only a few uninsulated columns but they are relatively
big (1.2m wide, 2m deep) and spaced by 8m or 18m. It doesn't seem
appropriate to me to give an overall U-value to the assembly, spreading the
effect of the columns over such "long distances". I'd rather model the
columns as surfaces separate from the surrounding walls, especially as
they are glazed curtain walls.

Patrick

---------- Forwarded message ----------

Patrick Bivona's picture
Offline
Joined: 2012-11-12
Reputation: 0

Joe & Mike's advice to use THERM is something I would support to convert a two dimensional heat transfer problem into one dimensional properties which most energy simulations are based on. We have good success with this method when looking at edge beams and band beams that in the past have not been continuously insulated and where the extended surface area is significantly different from the projected surface area.

I assume your column has insulation somewhere? While in annual energy terms the effect of insulating would be call if not a negative effect due to reduced free cooling, the effects in winter could be quite problematic. The column surface temperatures will be very cool in winter after a weekend and I doubt anyone could sit near them comfortably unless insulated or compensated in some way (temperature, radiant heating etc).

I have had a few projects over the year where band or edge beams between carparks and office spaces have not been continuously insulated. We have taken IR gun surface temperature measurements, modelled in THERM, taken THERM results to develop IES inputs and simulated remedial measures successfully and quite accurately relative to what the simulation would suggest.

Not knowing your climate zone, you can run different scenarios (boundary conditions and materials) in THERM to get a feel as to whether you have a radiant temperature asymmetry issue in winter.

So comfort not energy will (or should) govern the need to insulate...

Regards,
Graham

hamnmegs at ozemail.com.au's picture
Joined: 2011-10-02
Reputation: 0

Patrick,

Those are some mighty columns!

I think it depends on what you're trying to achieve with the model. If you're looking at radiant temperatures, local thermal comfort or similar, then I would agree that taking an area weighted approach is going to neglect important local differences due to thermal inertia and other factors. However, if you're looking at the energy use of the entire building, and it's conditioned 24 hours, or in a climate with negligible diurnal swing, or with limited thermal mass generally, I would still say that a simplified approach would give you results that are accurate enough. I concur with Joe on the point about thermal bridging. Particularly if the remainder if the fa?ade is insulated. Most construction inputs in energy modelling software don't accurately account for thermal bridging, so if you think they're going to be significant, then use a separate 2D calculation software and adjust your u-values appropriately.

That said, as they're relatively large and it's easy enough to divide up the walls into separate constructions, as it is with software like IES, then by all means model them separately and apply a different construction.

Much of the importance of the above is also dependant on the climate your build is in. E.g. Un-insulated concrete columns in a northern European climate are a terrible idea and will come with a big energy penalty. In warmer climates, their contribution to the overall energy of the building will be much smaller and your efforts on the accuracy of their modelling may be better spent looking at something like the fresh air or building leakage.

Regards,

Edwin Wealend

Wealend, Edwin's picture
Offline
Joined: 2013-02-18
Reputation: 0

Edwin, Graham,

Thanks for your advice. I had initially misunderstood what Joe was actually
proposing to do to take two dimensional conduction into account in and in
the vicinity of the columns. I'll follow his and your suggestion. It will
be a good learning experience for me anyway.

To answer your questions about the climate zone, this building is in South
Vietnam, so hot and humid all year around with some small variations. The
columns won't be insulated and the building will be air-conditioned. A nice
thermal bridge but not as bad as in a cold climate. Sadly, this is not the
type of project where the energy modelling is informing the design much...

Regards,
Patrick