I am wondering what others do for building zones that are conditioned but have no direct HVAC control. For example, a typical school will have a DOAS with perimeter radiation in exterior zones. There will be temperature and CO2 DCV in these occupied zones. The corridor will have transfer air and may have a couple of small supply diffusers from the DOAS but there is no thermostat to control the temperature in that corridor.
If there is no thermostat, there is no setpoint so how does one determine if the corridor has unmet loads? How would one model the corridor zone in the baseline case for Appendix G?
Christopher R. Jones, P.Eng.
Technical Specialist
Sustainability & Energy
[cid:image001.png at 01D3AC93.7A56DF80]
T +1 416-644-0252
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4 Canada
wsp.com
Please consider the environment before printing...
________________________________
NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited. If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl
AVIS : Ce message, incluant tout fichier l'accompagnant (< le message >), peut contenir des renseignements ou de l'information privil?gi?s, confidentiels, propri?taires ou ? divulgation restreinte en vertu de la loi. Ce message est destin? ? l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez re?u ce message par erreur, ou que vous n'?tes pas un destinataire autoris? ou voulu, veuillez en aviser l'exp?diteur imm?diatement et d?truire le message et toute copie ?lectronique ou imprim?e. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications ?lectroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap
-LAEmHhHzdJzBlTWfa4Hgs7pbKl
My opinion:
If there is no thermostat, the design essentially says that a wide
temperature variation is acceptable. You might consider arguing that those
zones *cannot *have unmet load hours because the design does not attempt to
control temperature.
For your own peace of mind (if your software allows it), you might also
report hourly temperatures in the zone to confirm that temps don't go crazy
unexpectedly during occupied hours.
Thanks Jim,
Your suggested approaches are in line with how I have been handing the issue.
Christopher R. Jones, P.Eng.
Technical Specialist
Sustainability & Energy
[cid:image001.png at 01D3AC98.5477A510]
T +1 416-644-0252
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4 Canada
wsp.com
Please consider the environment before printing...
Christopher,
I agree with Jim.
I typically model all conditioned spaces including semiheated spaces with heating and cooling thermostat schedules, except for heating-only zones that meet the criteria for Systems 9/10 in Appendix G, for which I leave the cooling thermostat schedule undefined. I may enter relaxed design conditions for zones that aren?t intended to have tight temperature control (using DESIGN-COOL-T and DESIGN-HEAT-T in DOE-2/eQUEST), and use correspondingly relaxed thermostat schedules for those zones. If there are unmet hours in the proposed design that I can?t address by relaxing the thermostat schedules even further, than I might leave the heating and/or cooling thermostat schedules undefined to represent floating with no thermostat control (which results in no reported unmet loads to have to explain). I keep all design conditions and thermostat schedules identical in the baseline as required by Appendix G.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image001.jpg at 01D3AC99.C5630110] [cid:image010.jpg at 01D3AC99.C5630110]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com www.pathfinder-ea.com
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
One should also point out that a corridor is a transient space and is
therefore not critical.
Peter Simmonds, Ph.D., FASHRAE, FIBPSA, FFTI
Mobile USA: +1-310-383-9911
Mobile HKG: +852-9227-1640
Mobile UK: +44 7470461689