So I have been reviewing my proposed energy model for LEED v4 certification
and I needed to check with someone if modeling the water-side HVAC system
with one boiler is acceptable instead of modeling two boilers, which are to
be designed in the final drawings, because of the fact that only one boiler
will operate at a time instead of both operating simultaneously (part load).

misterfolgers's picture
Offline
Joined: 2015-04-22
Reputation: 0

Hi Edgar,
I never model ?standby? or redundant pieces of equipment if they are identical and if they are designed and controlled for backup/emergency purposes and/or cycled only to distribute wear-and-tear across multiple components. This is typical for boilers and pumps. I often name the components in the model to reflect that there are more than one ? P-1/2, B-1/2 etc.
Regards,
~Bill

William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer

[Pathfinder-EA-logo-2]T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com www.pathfinder-ea.com
[cid:image006.png at 01D44436.F15A0B80]134 South Fitzhugh Street
Rochester, NY 14608 Ask me why Carbon Fee & Dividend may be right for you.