Folks:

I am modeling a chilled beam demonstration area. In one room the owner will be
installing a split AC system with electric heat in order to provide a false load
for the chilled beams.

The primary air to the 3 chilled beams is provided via VAV terminals from an
ERU. The ERU is equipped with chilled and hot water coils.

I can simulate a false cooling load by adding equipment under the Internal Loads
tab. I don't know how to make the room colder during the summer months in order
to require more heat from the chilled beams.

Any ideas on how to simulate a false heating load into this space?

Thank you,

Paul Diglio, CEM, CBCP

Paul Diglio's picture
Offline
Joined: 2011-09-30
Reputation: 400

Paul,

You should be able to model that by entering negative Input Power Btu/h
under Internal Energy Source on the Equipment tab of the Space Properties
window:

I used it on a few occasions to capture impact of externally calculated
process loads such as refrigeration equipment with remote condensers.

Maria

Maria Karpman's picture
Offline
Joined: 2011-09-30
Reputation: 0

Maria & David:

Thank you, I didn't know I could enter a negative value in Internal Energy
Source.

Paul Diglio, CEM, CBCP

Paul Diglio's picture
Offline
Joined: 2011-09-30
Reputation: 400