Metal frame walls

2 posts / 0 new
Last post

Hi Gang:
Every once in a while, a model appears.
I have forgotten how to do a metal frame wall with infill batt insulation. The wall is a 2 x 6 @ 24" centers with 6" R-19 insulation. I also know that there is 4 " board insulation continuous across the steel.?
Where can i go for the equivalent R-values?
Thanks in advance.
John Aulbach, PE

via Equest-users's picture
Joined: 2016-07-15
Reputation: 400

Hi John,
Per ASHRAE 90.1, Table A9.2-2, with R-19 between 6? framing @ 24? O.C., effective R-Value is R-8.6 for the frame/batt layer. Then add the R-Values of the continuous layers to get the assembly R-Value.
Regards,
~Bill

William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer

[cid:image001.jpg at 01D332E7.E5361F80] [cid:image002.jpg at 01D332E7.E5361F80]

134 South Fitzhugh Street Rochester, NY 14608

T: (585) 698-1956 F: (585) 325-6005

bbishop at pathfinder-ea.com www.pathfinder-ea.com

[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.

via Equest-users's picture
Joined: 2016-07-15
Reputation: 400