Hello,
My LS-C report is showing a zero number for a building with a roof area.
[cid:image001.png at 01CE1374.930C8B50]
I have looked at our model and I don't see where the roof is not being picked up.
MICHAEL RAIVA, P.Eng., LEED(r) AP, CCGD(r)
You should look at your LS-B for the plenum zone. Since eQUEST calculate heat transfer within the conditioned zone and unconditioned zone separately, heat loss through the roof should be included in the plenum zone if it's there.
You should look at your LS-B for the plenum zone. Since eQUEST calculate
heat transfer within the conditioned zone and unconditioned zone separately,
heat loss through the roof should be included in the plenum zone if it's
there.