Location of HVAC Equipment

2 posts / 0 new
Last post

Hello All,
Can anyone explain why after placing HVAC equipment such as a boiler in a
particular thermal zone that is unconditioned there are no visible changes
in space temperature while the equipment is operating. Does eQUEST not see
the boiler as an internal gain?

Thank You,

Niko Michael Kalinic

Niko Michael Kalinic's picture
Joined: 2011-09-30
Reputation: 0

Niko,

See the descriptions below from the DOE-2 help menu. Looks like the
boiler sees the zone, but the zone doesn't see the boiler.

Bill

LOCATION

Accepts a code-word that specifies the location of the boiler:

OUTDOOR The boiler is located outdoors.

ZONE The boiler is located within a zone.
Note that the program does not model any zonal heat gain from the
boiler. See ZONE-NAME keyword.

ZONE-NAME

Takes the U-name of the zone containing the heater when LOCATION = ZONE.
You must specify the zone; if not, LOCATION will default to OUTDOOR.
(Partially implemented; the program will use the zone temperature when
calculating the tank losses or the performance of a HEAT-PUMP water
heater, however these interactions do not have any effect on the zone
temperature. For heat-pump water heaters, this can result in serious
errors.)

William Bishop, EIT, LEED(r) AP

Bishop, Bill's picture
Offline
Joined: 2011-09-30
Reputation: 0