Inlet temperature schedule for DHW

4 posts / 0 new
Last post

Hi all,
Does anybody know why the 'Inlet temperature Schedule' field is not
active in detalied interface?
Although several options show up in the desplegable menu it seems as if
the interface doesn't react to them.
Thanks,

*Xavier Garc?a Casals*

=?ISO-8859-1?Q?Xavier_Garc=EDa_Casals?='s picture
Joined: 2011-09-30
Reputation: 0

Xavier,

You have to remove the entry for Inlet Temperature (50.5F) and then you can enter a temperature schedule. The help menu says that the default is the monthly ground temperature.

William Bishop, EIT, LEED? AP

Bishop, Bill's picture
Offline
Joined: 2011-09-30
Reputation: 0

Thanks Bill, but the problem is that the interface seems to not allow
removing the inlet temperature. If you just delete it, an error missage
promps up saying that 50?F is the minimum allowed, and comes back to the
50.5?F.
The manuals say that as long as a schedule is set in (DHW-INLET-T-SCH),
this would be the default (and therefore you woundn't need to remove the
entry for 'Inlet Temperature'.
Have you ever been able to introduce this schedule from within eQuest?
Regards,

*Xavier Garc?a Casals*

=?ISO-8859-1?Q?Xavier_Garc=EDa_Casals?='s picture
Joined: 2011-09-30
Reputation: 0

Try right click - "Restore Default" for the Inlet Temperature. Then you should be able to enter a schedule. I also have found that sometimes just clicking "Edit/View User Default" and clicking "OK" will let me change a value that is otherwise frozen.

William Bishop, EIT, LEED? AP

Bishop, Bill's picture
Offline
Joined: 2011-09-30
Reputation: 0