HVAC Config Doubt

3 posts / 0 new
Last post

Hi everyone, first let me apologize for all my questions, secondly according
ASHRAE I must use an VAV with PFP boxes for the baseline model, But I don?t
know how made that, the software don?t bring me the options, I?m really lost
in this!!!, please see image below, if you have any suggestion please let me
know it, thanks in advance.

Description: cid:image002.jpg at 01CC86B4.7C8359C0

Cordialmente,

Andr?s Franco U.

Andres Franco Usme MicroCAD S.A.S's picture
Joined: 2011-09-30
Reputation: 0

I don?t know how to do it in the Wizard, but if go into Detailed Data Edit
mode, you can switch your system type to ?Powered Induction Unit.? See
below:

It will by default ask you for a chilled water loop for cooling. If you
aren?t using chilled water you can create a default loop, switch the
system to DX cooling, and delete the loop.

Then that enables some new menus in the zone, under the ?Air Flow? tab:

Select Parallel PIU for parallel fan-powered boxes. On the right side of
the screen are the variables for the fan-box.

Nathan Miller, PE, LEED?AP

Nathan Miller's picture
Offline
Joined: 2011-09-30
Reputation: 200

Thank you so much!!!

Cordialmente,

Andr?s Franco U.