How to Model This?

2 posts / 0 new
Last post

Dear All,

How would you model the following: An office building in a cold climate
is cooled with air condenser chillers during summer, spring and autumn,
but with dry coolers during winter. The chillers will be completely off
when the dry coolers are running.

While trying, I have realized that I cannot assign any dry coolers (ie.
heat rejection) to the same circulation loop connected to the chillers.

Thanks,

Omer Moltay

Omer Moltay's picture
Offline
Joined: 2011-09-30
Reputation: 0

I had something similar to this before. I believe I made the chillers water cooled chillers and used the water-side economizer chiller and played with the performance curves to get close to what I needed. I also zeroed out any energy associated with the heat rejection. If anyone knows of a better way to simulate this I would be interested as well.

Charles Land's picture
Offline
Joined: 2011-09-30
Reputation: 0